someone raised a point about supplying an 11kw motor with a star/delta starter using two seperate armours for supply to motor 1 for run and one for star... I have never heard of this method being preferred and can find no reference to it anywhere has anyone else came accross thisText

#2 chaterpilar

chaterpilar

    Member

  • Full Member
  • PipPipPipPip
  • 171 posts

Posted 06 March 2006 - 03:55 AM

Chris,

use of 2 runs of 3 core armoured cable for Y/D starter is what it meant.

chaterpilar

#3 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,642 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 06 March 2006 - 05:33 AM

You need to have six cores from the starter to the motor. It is possible to use two three core cables, or six single core cables. Thus, the answer to your question is yes.

Best regards

#4 Chris57

Chris57

    Junior Member

  • Members
  • PipPip
  • 3 posts
  • Interests:just an ordinary guy still looking and still learning

Posted 06 March 2006 - 11:31 PM

Yes two three cores for y and d would give the six required but I would install 1 x 7 core this gives the option at a later date to utalise the seventh core as earth or a nuetral if for example a bulkhead fitting was required for an external motor My post really was asking was there any particular reason anyone could thinkof for using two seperate cables and thanks for the prompt replies and input

#5 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,642 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 07 March 2006 - 10:17 PM

Hi Chris57
The major reason is for identification, one cable connects to the start of each winding and to the main contactor and the other cable connects to the ends of each winding and to the delta contactor. Electrically, both options are staisfactory if you really must use a star/delta starter.