;p; hi guys i need help i have 15K watts inductive load what should i do to reduce my electrical bill??? is this ok that i will use a power capacitor w/c is 1farad 300v 120 Amps. my supply is 250V, 60 amps. RMS, pls me!!;p;

capacitor required
Started by CoE, Mar 27 2006 04:51 PM
3 replies to this topic
#1
Posted 27 March 2006 - 04:51 PM
#2
Posted 27 March 2006 - 06:33 PM
Hello CoE
Welcome to the forum.
An inductive load is OK and the inductive current will not add to your KWHr usage unles you have high losses in the feeder to it.
If you are paying for KWHrs only, I would not recommend power factor coreection unless you have a loading problem on your supply. If you are paying a power factor or a maximum demand penalty, then there may be a financial advantage in power factor correction the load.
In order to apply power factor correction, you need to establish what the level of inductive current is. The measured current will be a combination of inductive and resistive currents and you need to separate these out. There is instrumentation that will measure KVAR, or you can calculate it if you know the total current and power factor to that circuit.
Best regards,
Welcome to the forum.
An inductive load is OK and the inductive current will not add to your KWHr usage unles you have high losses in the feeder to it.
If you are paying for KWHrs only, I would not recommend power factor coreection unless you have a loading problem on your supply. If you are paying a power factor or a maximum demand penalty, then there may be a financial advantage in power factor correction the load.
In order to apply power factor correction, you need to establish what the level of inductive current is. The measured current will be a combination of inductive and resistive currents and you need to separate these out. There is instrumentation that will measure KVAR, or you can calculate it if you know the total current and power factor to that circuit.
Best regards,
Mark Empson | administrator
Skype Contact = markempson | phone +64 274 363 067
LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | Soft Starters
#3
Posted 31 March 2006 - 04:22 PM

so is thier a posibility that i could reduce my electrical bill?? by using a capacitor??
#4
Posted 31 March 2006 - 05:04 PM
Only if part of your utility bill includes a penalty for having poor power factor. It will not save on total kWH that they bill you for.