Hi,

We just overhauled a submersible pump and noted that two windings were burnt . Moreover, the thrust pads were found broken and the carbon seals severely weared. The motor is a 200 k W one. This was installed one year back and had hardly run.
Any clue.

Bob

#2 jraef

jraef

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 683 posts
  • Gender:Male
  • Location:USA, California

Posted 11 April 2006 - 05:24 PM

How are you starting / controlling the pump?
"He's not dead, he's just pinin' for the fjords!"

#3 bob

bob

    Member

  • Full Member
  • PipPipPipPip
  • 187 posts
  • Gender:Male

Posted 12 April 2006 - 04:02 AM

The motor is started through an auto-transformer starter. Besides all our submersible pumps are started this way.

Regards.

Bob

#4 jraef

jraef

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 683 posts
  • Gender:Male
  • Location:USA, California

Posted 12 April 2006 - 04:43 PM

Lots of possibilities, the best answer would come from someone analyzing the type of winding damage. Here is a simple guide:

EASA winding damage link

Could be that your auto-transformer is taking too long to transition into run, could be that your taps are too high so you have too much starting torque and therefore too much upthrust, could even have been hit by lightning!
"He's not dead, he's just pinin' for the fjords!"

#5 GGOSS

GGOSS

    Senior Member

  • Moderator
  • PipPipPipPipPip
  • 407 posts
  • Location:Melbourne

Posted 30 June 2006 - 06:27 AM

Most submersibles are designed for DOL starting, so I would find it difficult to believe that this could be the cause of damage.

Wear to the thrust pads tends to suggest not enough upthrust ie insufficient upthrust can result in insufficient lubrication of the thrust pad leading to wear. This would indicate that the AT tapping selected is too low.

Bob, it's been a while since you first raised this. Have you been able to identify the fault cause? What action has been taken to ensure it does not occur again?

Regards,
GGOSS

#6 bob

bob

    Member

  • Full Member
  • PipPipPipPip
  • 187 posts
  • Gender:Male

Posted 03 July 2006 - 04:22 AM

Hi GGoss,

Thanks for your concern. We sent the motor and pump assembly back to Italy and although they did not claim that it was a design problem, they agreed to send us back a new one. We have not yet completed the installation. You are right , we have got plenty of submersible pumps which are D.O.L started and which are still in operation since years.

Bob

#7 GGOSS

GGOSS

    Senior Member

  • Moderator
  • PipPipPipPipPip
  • 407 posts
  • Location:Melbourne

Posted 05 July 2006 - 04:16 AM

Hi Bob,

Your very welcome.

It does sound like they are aware of a design/manufacturing problem.

Submersible motors are a wonderfull thing, particularly those fitted with thrust bearings. When applying a reduced voltage starter, be it electronic or otherwise there is always some compromise required. Start the pump slowly to minimise fluid hammer and there's a chance that the thrust bearings will fail prematurely. Start it more quickly to minimise damage to the thrust bearings and introduce water hammer.

I'm not sure if there's a single answer for every application. In my experience each needs to be handled/addressed on a case by case basis.

Hope this installation goes well for you.

Regards,
GGOSS

#8 mariomaggi

mariomaggi

    Senior Member

  • Full Member
  • PipPipPipPipPip
  • 234 posts
  • Gender:Male
  • Location:Milan, Italy
  • Interests:electric vehicles http://www.evlist.it , 3-phase AC sources to test PV inverters, high-power AC/DC power supplies up to 1500 VDC to test photovoltaic inverters, bidirectional AC/DC power supplies to test and simulate big batteries, infrared windows for thermography, renewable energies, special electric motors, special inverters, energy savings, power quality

Posted 06 July 2006 - 08:19 PM

Dear bob,
QUOTE
We sent the motor and pump assembly back to Italy and although they did not claim that it was a design problem, they agreed to send us back a new one.


Free substitution? I've found some cases in which the manufacturer is not able to explain what happened, and prefer to lose some money substituting the unit. Not all manufacturers have enough statistics on their motors to be in position to give a sure report on damages.

Regards
Mario