Is the detuning reactor can help limit possible current and voltage peaks on critically corrected motor? Capacitor connected directly to motor cable (static correction).

detunig reactor and critically corrected motor
Started by frs, May 11 2006 07:13 AM
1 reply to this topic
#1
Posted 11 May 2006 - 07:13 AM
#2
Posted 11 May 2006 - 07:28 AM
Hello frs
Welcome to the forum
Ading a detuning reactor to a critically corrected motor will shift the resonant frequency down below line frequency which is not good as when the motor is disconnected, it will slow down and pass through the resonant frequency.
The best solution is to correct ot 80% of the magnetising current only, and use a separate contactor to control the power factor correction capacitors.
Best regards,
Welcome to the forum
Ading a detuning reactor to a critically corrected motor will shift the resonant frequency down below line frequency which is not good as when the motor is disconnected, it will slow down and pass through the resonant frequency.
The best solution is to correct ot 80% of the magnetising current only, and use a separate contactor to control the power factor correction capacitors.