Q1. How to measure by calculation and by meter the inrush current flow in series reactor?
Q2.Where the harmonics come from?Because this capacitor bank is located at HTSWGR panel and supply to motors etc.
Q3.Oil type reactor explode may be due to not enough capacity of the reactor itself?.
Q4.If I use dry type reactor instead of oil type reactor is it more practical?
Q5.What is the best preventive maintenance for this Capacitor bank panel?
Thank you for your help.

series reactor
Started by kuan, Sep 22 2002 10:46 AM
1 reply to this topic
#1
Posted 22 September 2002 - 10:46 AM
#2
Posted 24 September 2002 - 08:08 PM
Hello kuan
Where the harmonics come from?Because this capacitor bank is located at HTSWGR panel and supply to motors etc.
Harmonics are always present on the supply and com from many different types of equipment connected to tne supply. Some harmonics are introduced by iron cored items such as motors and transformers, but by far the greatest source of harmonics are electronic rectifiers as found in inverters and switched mode power supplies. Arc furnaces are another large source of harmonics. These harmonics are caused by the non sinusoidal current drawn by the connected load. If the supply impedance is very low, then the effect of harmonic currents on the supply voltage is reduced.
Oil type reactor explode may be due to not enough capacity of the reactor itself?.
Correct, if the reactor is overloaded, it will overheat.
If I use dry type reactor instead of oil type reactor is it more practical?
You still have the problem of overloading the reactor if it is not big enough. The oil filled reactor can use smaller components internally because the oil helps to increase the effective cooling area. For large units, oil filled are smaller. For small units, there may be little advantage.
QUOTE
Where the harmonics come from?Because this capacitor bank is located at HTSWGR panel and supply to motors etc.
Harmonics are always present on the supply and com from many different types of equipment connected to tne supply. Some harmonics are introduced by iron cored items such as motors and transformers, but by far the greatest source of harmonics are electronic rectifiers as found in inverters and switched mode power supplies. Arc furnaces are another large source of harmonics. These harmonics are caused by the non sinusoidal current drawn by the connected load. If the supply impedance is very low, then the effect of harmonic currents on the supply voltage is reduced.
QUOTE
Oil type reactor explode may be due to not enough capacity of the reactor itself?.
Correct, if the reactor is overloaded, it will overheat.
QUOTE
If I use dry type reactor instead of oil type reactor is it more practical?
You still have the problem of overloading the reactor if it is not big enough. The oil filled reactor can use smaller components internally because the oil helps to increase the effective cooling area. For large units, oil filled are smaller. For small units, there may be little advantage.
Mark Empson | administrator
Skype Contact = markempson | phone +64 274 363 067
LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters
0 user(s) are reading this topic