On a VSD it is standard to use a screened cable like Varolex or similar. But what about for a soft starter,
they are 'on-line' only during start-up, so is a screened cable still neccesary?

#2 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,601 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 12 August 2006 - 04:21 AM

Hello bodolman

Welcome to the forum

No, it is not necessary to use screened cable with soft starters. With VFDs, there is considerable EMC radiation due to the high speed switching of the output devices. Soft starters do not use this technology and so do not have these problems.