Hi,

Ive got two 400 kW 400 V VSDs powered from the same transformer. The drives are equipped with multiple cooling fans to cool the heat sink. The cooling fans are rated 24 V dc. The power supplies are powered by the 400 V supply of the VSD and each power supply has got a 15 A fuse on the secondary side of their transformer. We had two power shutdowns and at each time the 15 A fuses blew. The fuses were replaced and the power supplies resumed back to operation. Its a pity that at each time the VSDs tripped on high temperature because they dont have any means to know that the fans were not operating. Furthermore, it took us a lot of times to replace the fuses because the power supplies are located inside the enclosure which had to be removed before.
It is also worth metioning that we have a lot of VSDs, UPS, power supplies, PLCs working on the site and no problem were noted on these equipments.
Any guess ?

Bob

#2 mariomaggi

mariomaggi

    Senior Member

  • Full Member
  • PipPipPipPipPip
  • 230 posts
  • Gender:Male
  • Location:Milan, Italy
  • Interests:electric vehicles http://www.evlist.it , 3-phase AC sources to test PV inverters, high-power AC/DC power supplies up to 1500 VDC to test photovoltaic inverters, bidirectional AC/DC power supplies to test and simulate big batteries, infrared windows for thermography, renewable energies, special electric motors, special inverters, energy savings, power quality

Posted 17 September 2006 - 05:55 AM

Dear bob,
it is clear that 15 A fuses are not properly selected for that application.
You don't mention the nominal current in this circuit, and the type of fuse (fast, slow, etc.), therefore I cannot give a more precise suggestion.
Probably such brushless fans have inside a capacitor, during "bursts" in the transients the I2t of such fuses was not enough high.

Another possibility, for certain types of fuses: corrosion due to bad ambient conditions. In this case such fuses are no more rated 15 A, but less. During normal running there are no problems, but during restarting the fuses blows.

If possible, you could add another power supply in parallel - with output rectifiers - probably it cost less than a long stop of such machine!

Regards
Mario

Mario Maggi - Italy - http://www.evlist.ithttps://www.axu.it


#3 bob

bob

    Member

  • Full Member
  • PipPipPipPip
  • 187 posts
  • Gender:Male

Posted 17 September 2006 - 08:10 AM

Dear Mario,

Many thanks for your very quick reply. Yes, the ceramic fuses blew during transient. We operate in parallel with the grid and under two occasions when we lost the grid , the fuses blew off. It is also worth mentioning that we have on site many different makes of power supplies and only these two behave like this.
It is quite normal that the network experience a surge condition during a sudden suppression of load( 12 MW ) but I believe the fuses are wrongly rated under these conditions.

Regards.

SSooben

#4 mariomaggi

mariomaggi

    Senior Member

  • Full Member
  • PipPipPipPipPip
  • 230 posts
  • Gender:Male
  • Location:Milan, Italy
  • Interests:electric vehicles http://www.evlist.it , 3-phase AC sources to test PV inverters, high-power AC/DC power supplies up to 1500 VDC to test photovoltaic inverters, bidirectional AC/DC power supplies to test and simulate big batteries, infrared windows for thermography, renewable energies, special electric motors, special inverters, energy savings, power quality

Posted 17 September 2006 - 10:35 AM

Dear bob,

QUOTE
I believe the fuses are wrongly rated under these conditions.


sure, if you can exclude strange situations like animals in the fans or adhesive liquids in the fan.

Regards
Mario

Mario Maggi - Italy - http://www.evlist.ithttps://www.axu.it