Posted 31 January 2007 - 07:53 PM
Sorry, I just learned something new today. I now work for Siemens, and in looking up our capacitor switching ratings, it appears that there is a slight difference in the construction of the contacor. For capacitor switching they have a set of "early make" (leading NO) aux contacts that place a resistor in parallel with each pole just immediately prior to the main contacts closing. This is to absorb the spike that occurrs as the capacitor is charged. Also, there is an IEC utilization catagory assigned to the contactors themselves, so you can look up any contactor and determine all AC ratings. In Siemens case, the S3 contactor is rated for 65kVAR at 400V according to AC-6b (capacitor switching duty), and also 45kW motors according to AC-3. So when used in a Start-Delta control scheme, the motor could be up to 80kW at 400V. I would imagine ABB and others are similarly rated although you may need to extrapolate the numbers since your contactor is ratred only for 60kVAR. If your contactors have the early-make aux contacts and resistors on them, be sure to remove them when using a on a motor.
AB2005,
I don't know about other brands, but if you can get hold of a Siemens catalog, look up the 3RT16 contactors for a description of how they work and a link to wiring diagrams, ratings etc.
"He's not dead, he's just pinin' for the fjords!"