Posted 29 May 2007 - 12:54 PM

hi
i want to know how to calculate overload setting for motor AC

hi
if the AC motor have 55 KW,how we can calculate for overload setting

#2 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,564 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 30 May 2007 - 02:20 AM

Hello amiruddin

You set the overload relay setting to the same as the rated current of the motor.
Best regards,

#3 rene4538

rene4538

  • Members
  • Pip
  • 1 posts

Posted 29 June 2007 - 01:50 PM

QUOTE(amiruddin @ May 29 2007, 12:54 PM)  

hi
i want to know how to calculate overload setting for motor AC

hi
if the AC motor have 55 KW,how we can calculate for overload setting


You can also calculate using the this formula P=I.E ,p=power ,I=current ,E=volatge then you can get the approximate motor current rating.Correct me if i am wrong.

best regards


#4 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,564 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 29 June 2007 - 02:14 PM

Hello rene4538

You have not taken into account the power factor or the efficiency which can have a major influence.

P = V x I x eff x pf

The power rating of the motor is the shaft power, not the electrical power.
The best way to determine the current rating, is to look at the motor name plate. - always shows the current rating.

Best regards,

#5 AB2005

AB2005

    Senior Member

  • Full Member
  • PipPipPipPipPip
  • 398 posts

Posted 30 June 2007 - 06:21 AM

Normally, motors are selected 120% greater power than load. So, first, we check how much motor draws the current at the maximum working speed of machine which should be lesser than motorís maximum current typed on the name plate. Now you can set the overload slightly at higher current under the motor full load current. This will also save your motor and your load.
"Don't assume any thing, always check/ask and clear yourself".

#6 Nitin

Nitin

  • Members
  • Pip
  • 1 posts

Posted 30 June 2007 - 09:19 PM

QUOTE(amiruddin @ May 29 2007, 06:54 PM)  

hi
i want to know how to calculate overload setting for motor AC

hi
if the AC motor have 55 KW,how we can calculate for overload setting

hi
first U measure current with clampon meter and then increase relay setting 5 amp more than that.

#7 chaterpilar

chaterpilar

    Member

  • Full Member
  • PipPipPipPip
  • 171 posts

Posted 05 September 2007 - 03:34 AM

Dear Amirudin,

The more the data you will give in the question the more closer the answer will be.

For example 55 kw, at what what voltage 380 volts, 415 volts, 690 volts..?

Let us say it is a 415 volts rated motor.

In case of a star-delta starter the location of overload relay matters a lot, it can be located where 100% of current is passing through the relay or 58%is passing through.

For sake of calculation, if the motor name plate rating is 100 amps, then follow these steps.

1. Set the relay at 58 amps and start the motor and

2.Check the current at the output of relay with a clampon meter after the motor is running at its full speed and full load.

3.Let us say it is 43 amps, then set relay 3amps above 43 that is 46 amps.

A properly designed motor should have OLr setting at 80% of its full load current ( @ Name plate )

Hope it helps.

Good Luck !!


Chaterpilar



#8 pelia

pelia

  • Members
  • Pip
  • 1 posts

Posted 13 September 2007 - 11:17 PM

QUOTE(amiruddin @ May 29 2007, 05:54 AM)  

hi
i want to know how to calculate overload setting for motor AC

hi
if the AC motor have 55 KW,how we can calculate for overload setting


for the overload setting
1
a) 125% of the full load current rating of a motor having a marked service factor of 1.15 or greater
cool.gif 115% of the full load current rating of the motor which does not having a marked service factor or where the service factor is less than 1.15
2
where a motor overload device is so connected that it does not carry the total current designated on the motor name plate , such as for wye-delta starting , the percentage of the motor nameplate crrent applying to the selection or setting of the overload swhall be clearly marked on the motor starter shown in the motor starter manufacturs overload selection table


#9 SNSwamy

SNSwamy

    Junior Member

  • Members
  • PipPip
  • 2 posts

Posted 11 February 2008 - 05:39 PM

QUOTE (amiruddin @ May 29 2007, 06:24 PM) <{POST_SNAPBACK}>
hi
i want to know how to calculate overload setting for motor AC

hi
if the AC motor have 55 KW,how we can calculate for overload setting



find the actual running of the motor Check the voltage.depending on the load set the relay to that load if it is less than full load & if the load is more than full load set the relay at full load of motor


#10 Bysikmode

Bysikmode

    Intermediate Member

  • Full Member
  • PipPipPip
  • 11 posts

Posted 20 April 2014 - 01:06 PM

thanks for the info guys. it'll really help me.



 