AC Drives are sold with voltage ratings and HP ratings ,

now, my question is will a 40 hp 460 volts 60hz variable speed drive be suitable to be used in a place having 380volts 60 hz power supply to drive a 40 hp/380 volts motor.

I feel drive has to be derated by 17%.

Any thoughts..



#2 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,603 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 15 January 2008 - 06:08 PM

Hello chaterpilar

There are two issues here.
1. Will the drive operate on 380 volt? and 2. what will the rating be.

1. Most modern drives operate all the electronics from a switch mode supply off the DC bus so there should bee no problem operating the electronics off the lower voltage except that the under voltage and over voltage trip settings will need to be altered. You would need to talk to the supplier about doing that.

2. The real rating of the drive is not power, it is current. When you reduce the supply voltage, the current will stay the same, so the power rating will drop by the same amount as the current.

If you are looking for a unit to operate on 380 volt 60Hz, you could use any drive designed for the European market. The 50 Hz or 60Hz on the input will make no difference to the operation of the drive.

Best regards,

#3 amit kumar

amit kumar

    Junior Member

  • Full Member
  • PipPip
  • 5 posts

Posted 16 January 2008 - 03:28 AM

See the operating voltage range of drive.If it is within your requirement,you can run drive at different voltage.
Otherwise it is not advisable to operate the drive beyond the specified voltage range.