pfc caps and vsd for plastic injection machines
#1
Posted 27 February 2003 - 03:06 AM
#2
Posted 27 February 2003 - 09:05 AM
welcome to the forum.
pfc capacitors are used to improve the power factor of induction motors and thereby reuce any power factor or KVA penalty that you may be paying. They will not reduce the kw drawn by the motor. If you use a vsd, you can not use pfc capacitors. pfc capacitors across the motor will cause the vsd and/or the capacitors to fail! You must use either one or the other but not both.
Best regards,
Mark Empson | administrator
Skype Contact = markempson | phone +64 274 363 067
LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters
#3
Posted 27 February 2003 - 10:50 PM
or can i have a vsd and still use bulk pf correction?
#4
Posted 02 March 2003 - 09:57 AM
To give you a definative answer, we would need to have a lot more information.
Fitting a VSD will only save energy if you are going to operate the motor at reduced speed. I would expect that this is not the case in this application, so you could actually end up using more energy by fitting the VSD.
Yes, you can use a VSD and still have bulk correction at the point of supply, but the input current to the VSD is very rich in harmonic currents and could cause an increase in the capacitor current and premature capacitor failure. I would recommend that if you are using bulk correction on the same supply as you have VSDs connected, that you fit detuning inductors to the capacitors.
Best regards,
Mark Empson | administrator
Skype Contact = markempson | phone +64 274 363 067
LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters
#5
Posted 30 October 2003 - 01:14 PM
#6
Posted 30 October 2003 - 01:43 PM
The reactor is an inductor, so yes they are the same thing.
Best regards,
Mark Empson | administrator
Skype Contact = markempson | phone +64 274 363 067
LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters
#7
Posted 06 February 2004 - 02:18 AM
you must take a look the harmonic thd. by installing pfc you might be magnifying the distortion.