Vfd For Compressor
#1
Posted 19 June 2008 - 07:00 AM
I want to use VFD for a 75KW motor air copressor unit. I have Presure feedback as 4-20 mA. How i can use this f/b to do this application? Loading is around 60%.
Regards
Rahul
#2
Posted 21 June 2008 - 09:11 PM
I assume that you wish to run at a constant pressure.
To operate the VFD at a constant pressure, enable the PID control within the drive and use in internal or external reference to set the pressure as the PID set point, and use the pressure transducer as the feedback for the PID.
I do not know which drive you are using, but I am sure that if you refer to the manual, you will see how to achieve this.
I can give examples for the Emotron and Control Techniques drives if you are stuck.
Best regards,
Mark.
Mark Empson | administrator
Skype Contact = markempson | phone +64 274 363 067
LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters
#3
Posted 04 March 2011 - 06:40 PM
i have same application in emotron ac drive if you can provide me detail about configuration in emotron ac drive
#4
Posted 04 March 2011 - 08:38 PM
Best regards,
Mark.
Mark Empson | administrator
Skype Contact = markempson | phone +64 274 363 067
LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | AuCom | Soft Starters