Jump to content


Photo

SINGLE PHASE SOFT STARTER


  • Please log in to reply
6 replies to this topic

#1 DEVITG

DEVITG

  • Members
  • Pip
  • 1 posts
  • Location:CORDOBA

Posted 24 May 2003 - 11:19 PM

It is posible to use a soft starter on a single phase motor ?

It is for two semihermetic refrigeration motocompresor , with current relay as start device.

The main problem is that it is installed on a truck with a generator .
The full load amp is 9- 11 amps. 220 V 50 Hz.
The generator is a 16 HP briggstraton with a 8 KVa.
It can start and run only one , but it will not star the second unit.

#2 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,604 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 25 May 2003 - 12:07 AM

Hello devitg

Yes it is possible to use a soft starter on a single phase motor.
It needs to be a single phase soft starter, and will work best on capacitor start motors. From my experience, soft starters do not work as well on induction start motors.
Unfortunately, I can not at present suggest a manufacturer of a single phase soft starter.

Best regards,

#3 GGOSS

GGOSS

    Senior Member

  • Moderator
  • PipPipPipPipPip
  • 407 posts
  • Location:Melbourne

Posted 02 June 2003 - 06:23 AM

Hello Devitg,

Can you please advise motor details ie operating voltage, rated current etc. Once we have these details we'll do our best to put you onto a possible supplier.

Regards,
GGOSS

#4 Guest_DEVITG01_*

Guest_DEVITG01_*
  • Guests

Posted 02 June 2003 - 10:39 PM

It is for two semihermetic refrigeration motocompresor , with voltimetric relay as start device.
160 mF Start capacitor
65mF Run Capacitor


The main problem is that it is installed on a truck with a generator .
The full load amp is 9- 11 amps. 220 V 50 Hz.
The generator is a 16 HP briggstraton with a 8 KVa.
It can start and run only one , but it will not star the second unit.

#5 jraef

jraef

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 683 posts
  • Gender:Male
  • Location:USA, California

Posted 16 October 2006 - 04:28 PM

Hi,

I resurrected this thread only because the subject of soft starting single phase motors came up for me recently, and I stated that you could NOT start a cap-start motor because of the problems of having capacitors down stream of the SCRs. The motor manufacturer contradicted me and in searching for support information, I read this. Now I am wondering if I was wrong (horror of horrors!) How is it that the starting capacitors are not a problem on 1 phase motors? Is it because the motor winding inductance in in series with it?
"He's not dead, he's just pinin' for the fjords!"

#6 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,604 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 16 October 2006 - 06:50 PM

Hello jraef

I have soft started many single phase motors with cap start without problems.
You can apply the soft starter to the whole motor (including cap and start winding) or apply the soft starter to the run winding only.
My preferred method is to the run winding only as you get a greater reduction in start current.
I have not had any issues with either the capacitors failing, or the soft starter failing due to the capacitor.
The only single phase motors that I will not soft start are induction start. (no capacitor) as they rely on iron saturation effects and just do not perform with soft starters.

Best regards,

#7 GGOSS

GGOSS

    Senior Member

  • Moderator
  • PipPipPipPipPip
  • 407 posts
  • Location:Melbourne

Posted 17 October 2006 - 12:11 AM

Care must be taken, ie in cases where the start voltage is set so low that the motor labours we have experienced problems with the capacitors and on fewer occasions, the centrifugal switch.

Another issue is that of 480V single phase motors intended for SWER line applications. These generally comprise 2 x 240V windings connected in series, the caps are also 240V rated. Through a simple voltage divide you will find that if the start voltage is set below 50%, the capacitor will experience an overvoltage condition until the voltage ramps above that point. capacitors can and do fail quickly under this condition.

In the main however, applying single phase soft starters to cap start or cap start cap run motors with flly rated windings and capacitors does not present an issue. There are companies established throughout Australia that literally sell thousands of them for use in domestic and light commercial air conditioning systems. Another common application particularly throughout WA is bore pumps.

Regards,
GGOSS