IS THERE ANY CHANCE OF SUCCESS OF SOFT STARTER IN CRANE TRAVEL APPLICATION WHERE NO.OF START / STOP IS SEVERE?? GENERALLY CRANE MOTORS RATED FOR 150ST/HR & 40% CDF. IF YES, THEN WHAT WILL BE THE SPECIFICATION OF SOFT STARTERS???
THANKS IN ADVANCE.
MY EMAIL ID IS dip04051978@yahoo.com.

soft starters for crane travel application??
Started by dip04051978, Aug 16 2003 04:39 AM
1 reply to this topic
#1
Posted 16 August 2003 - 04:39 AM
#2
Posted 16 August 2003 - 10:08 PM
Hello dip04051978
Yes, I have used soft starters in this application many times with no problems.
You must make sure that the soft starter is rated for the number of starts at the required start current and start duration. If you do not rate it correctly, you will have a prematue failure.
Best regards,
Yes, I have used soft starters in this application many times with no problems.
You must make sure that the soft starter is rated for the number of starts at the required start current and start duration. If you do not rate it correctly, you will have a prematue failure.
Best regards,
Mark Empson | administrator
Skype Contact = markempson | phone +64 274 363 067