WHAT WILL HAPPEN IF VFD IS CONNECTED ON MOTOR WHERE ALREADY PF CORRECTION CAPACITOR CONNECTED.
What will be the effect on Soft starter with the same case ??

#2 jraef

jraef

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 683 posts
  • Gender:Male
  • Location:USA, California

Posted 19 December 2008 - 11:46 PM

QUOTE (dip04051978 @ Dec 18 2008, 02:50 AM) <{POST_SNAPBACK}>
WHAT WILL HAPPEN IF VFD IS CONNECTED ON MOTOR WHERE ALREADY PF CORRECTION CAPACITOR CONNECTED.
What will be the effect on Soft starter with the same case ??

Usually a race between the capacitor or the power switching devices to see which one can fail faster.
"He's not dead, he's just pinin' for the fjords!"

#3 dip04051978

dip04051978

    Intermediate Member

  • Full Member
  • PipPipPip
  • 20 posts
  • Location:Anand

Posted 22 December 2008 - 05:44 AM

Thanks for rpely Jreaf.
We know it is not recommanded to connect capacitor on the output side of the Drive / Softstarter.
But can you please explain in detail how it will fail.

#4 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,603 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 23 December 2008 - 12:57 AM

Every time you turn ON the IGBTs in a VFD or the SCRs in a soft starter, they have to carry the charging current to the capacitors which look like a short circuit until charged.
This causes very high currents to flow through the switching device and these high currents damage the switching devices (IGBT SCR)

Best regards,
Mark.