Dear Friends;
I have recieved a mail from a company that they worked a project where they replaced the DOL and star delta starters with inverters and saved energy. They sent me following example of this change;
"Please find the energy saving report finalized after implementation:
1)- 767M2265
Motor Rating: 37KW
Load taken when DOL: 29Amps
Load taken when Drive: 8 Amps
Saving in current: 21Amps
Energy saved: 1.732*500*11*0.9=16KW
2)- 767M1507
Motor Rating: 22KW
Load taken when DOL: 25Amps
Load taken when Drive: 13 Amps
Saving in current: 12Amps
Energy saved: 1.732*500*12*0.9=9.3KW
3)-767M1776
Motor Rating: 18.5KW
Load taken when DOL: 19Amps
Load taken when Drive: 3 Amps
Saving in current: 16Amps
Energy saved: 1.732*500*16*0.9=12.5KW"
This is a strange think for me that how can it possible. I would have a meeting with them but first i need to verify from experts.
Energy Saving By Using Inverters In Place Of Dol
Started by AB2005, Dec 14 2011 10:03 AM
1 reply to this topic
#1
Posted 14 December 2011 - 10:03 AM
"Don't assume any thing, always check/ask and clear yourself".
#2
Posted 15 December 2011 - 08:11 AM
Hello AB2005
First of all, the calculations are not correct as you can not assume that the power factor is high.
In the calculations, I assume that the supply voltage is 500V ??
That is an unusual voltage.
The application is not described. What is the application or is it an open shafted machine.
A VFD will reduce the energy consumption only if the machine has significant mechanical losses at full speed, and does not need to operate at full speed to do the same amount of work.
The saving is the reduction in mechanical losses when the machine speed is reduced.
Calculated savings based on calculated values from measured Amps never work out correctly.
Many VFD suppliers claim energy savings in ALL applications using VFDs.
If the motor operates at full speed with a VFD in ccircuit, the energy consumed is higher than DOL.
The VFD has losses in the order of 3% - 5% plus the motor losses will increase due to the wave shape of the voltage applied to the motor.
The current into the VFD will be less than the current into the motor because the displacement power factor is better than 0.95 at the input of the VFD, irrespective of the displacement power factor at the motor.
Best regards,
Mark.
First of all, the calculations are not correct as you can not assume that the power factor is high.
In the calculations, I assume that the supply voltage is 500V ??
That is an unusual voltage.
The application is not described. What is the application or is it an open shafted machine.
A VFD will reduce the energy consumption only if the machine has significant mechanical losses at full speed, and does not need to operate at full speed to do the same amount of work.
The saving is the reduction in mechanical losses when the machine speed is reduced.
Calculated savings based on calculated values from measured Amps never work out correctly.
Many VFD suppliers claim energy savings in ALL applications using VFDs.
If the motor operates at full speed with a VFD in ccircuit, the energy consumed is higher than DOL.
The VFD has losses in the order of 3% - 5% plus the motor losses will increase due to the wave shape of the voltage applied to the motor.
The current into the VFD will be less than the current into the motor because the displacement power factor is better than 0.95 at the input of the VFD, irrespective of the displacement power factor at the motor.
Best regards,
Mark.
Mark Empson | administrator
Skype Contact = markempson | phone +64 274 363 067
LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | Soft Starters
Skype Contact = markempson | phone +64 274 363 067
LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | Soft Starters
1 user(s) are reading this topic
0 members, 1 guests, 0 anonymous users