Jump to content


Photo

Frequency And Torque


  • Please log in to reply
2 replies to this topic

#1 yuri

yuri

    Member

  • Full Member
  • PipPipPipPip
  • 93 posts

Posted 05 October 2012 - 06:54 PM

Hello
Can someone say me in which case the torque of an induction motor starting at lowered voltage will be higher :
1. When the voltage frequency is not changed
2. Or when the frequency is proportionally lowered ?

#2 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,618 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 06 October 2012 - 06:10 AM

Hello Yuri

If you reduce the voltage and keep the frequency constant, then the V/Hz ratio is reduced, the flux in the iron is reduced and the torque is also reduced.
If you reduce the voltage and frequency proportionally, the V/Hz ratio remains constant and the troque does not change.

Best regards,
Mark.

#3 yuri

yuri

    Member

  • Full Member
  • PipPipPipPip
  • 93 posts

Posted 06 October 2012 - 07:12 PM

Hello Mark !
Thank you very much, I also thought so, you confirmed it (was a bit in a doubt about that however)
My best regards




0 user(s) are reading this topic