#1 FbJavier

FbJavier

    Junior Member

  • Members
  • PipPip
  • 2 posts
  • Location:iligan city, philippines
  • Interests:fields of practice: electromechanical, electrical equipment, technical and engineering services

Posted 11 July 2002 - 08:37 AM

hello!
anyone who experience in balance impedance testing using surge comparison tester, id experience testing on 1.) DC armature winding with a rated armature voltage of 650V upon gradually applying the test voltage id notice at 250V, its wave signature distorts with tracking trace as shown on display but as i increase the the voltage over 250V it will then balance without distortion. is there something wrong in the winding? is there any test equipment that is more suitable for armature winding test? (its history has a pitch bar marking on commutator bars, no shorted nor open winding upon using growler) 2.) upon testing a 4160V (flat-wire coil) squirrel cage induction motor, id noticed a HISSING sound in the stator winding before its wave signature distorts to more chaotic trace. What makes this HISSING sound? Can anyone elaborate the occurrence of this phenomena, its posssible threat to the motor winding?

Thanks..


fbJavier

#2 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,642 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 14 July 2002 - 10:41 PM

I wonder if the "hissing" sound is a discharge in the winding, possibly caused by moisture. I would try drying out the winding well and repeating the test.

#3 electricpete

electricpete

    Junior Member

  • Members
  • PipPip
  • 6 posts

Posted 21 September 2003 - 11:18 PM

QUOTE
Originally posted by FbJavier
hello!
 anyone who experience in  balance impedance testing using surge comparison tester, id experience testing on 1.) DC armature winding with a rated armature voltage of 650V upon gradually applying  the test voltage id notice at 250V, its wave signature distorts with tracking trace as shown on display but as i increase the the voltage over 250V it will then balance without distortion. is there something wrong in the winding? is there any test equipment that is more suitable for armature winding test? (its history has a pitch bar marking on commutator bars, no shorted nor open winding upon using growler) 2.) upon testing  a 4160V (flat-wire coil)  squirrel cage induction motor, id noticed a HISSING sound in the stator winding before its wave signature distorts to more chaotic trace. What makes this HISSING sound? Can anyone elaborate the occurrence of this phenomena, its posssible threat to the motor winding?

1 - This sounds to me like a thresh-hold failure. At 250 volt surge level the turn insulation is breaking over.
2 - I have seen the Baker and PJ equipment used. Often when there is exposed metal connections we hear distinct clicking around twice a second as they flashover... I think it corresponds to the repetitive surge rate. I have never heard continuous buzzing or hissing in surge test... only in ac hi-pot test. What tester do you use?