Do I have to place some [start count per hour] limit for motor starters with static correction?
On the picture http://www.lmphotoni...om/pwrfact4.jpg capacitor is connected upstream of overload relay. Is it possible to connect capacitor downstream of overload relay (between overload relay and motor) ?
Can I use static correction for star-delta starters? Or motor get overcompensated in star connection?

Static correction
Started by
Guest_Anonymous_*
, Dec 04 2004 05:13 PM
1 reply to this topic
#1
Guest__*
Posted 04 December 2004 - 05:13 PM
#2
Posted 05 December 2004 - 01:53 AM
Hi
The addition of power factor correction does not alter the maximum number of starts per hour of the motor.
If you connect the power factor correction downstream of the overload relay, the current through the relay will be lower and the protection will not protect the motor.
Yes, you can use static correction for star-delta starters. This is commonly done.
If you register on the forum, you can receive email notification of replies.
Best regards,
The addition of power factor correction does not alter the maximum number of starts per hour of the motor.
If you connect the power factor correction downstream of the overload relay, the current through the relay will be lower and the protection will not protect the motor.
Yes, you can use static correction for star-delta starters. This is commonly done.
If you register on the forum, you can receive email notification of replies.
Best regards,
Mark Empson | administrator
Skype Contact = markempson | phone +64 274 363 067
LMPForum | Power Factor | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | Pressure Transducers | Smart Relay | GSM Control | Mark Empson Website | Soft Starters
0 user(s) are reading this topic
0 members, 0 guests, 0 anonymous users