sprecher + schuh CET4 Overload


  • Please log in to reply
1 reply to this topic

#1 phild

phild

    Intermediate Member

  • Full Member
  • PipPipPip
  • 10 posts
  • Interests:Electrician of sorts now expected to do everything, working in a once fabulous washery in the hunter valley. But like everything else we have been downsized and rationalised

Posted 06 December 2004 - 10:22 AM

Hello

Does anyone know of how to change the analogue output through the menu to be used as motor current reading to a PLC from a CET4.
From what I have read 100 % equals 12 mA.
I have had a look through the setup and can't see the parameter to enable or disable.


There are three possibilities.

Analog output motor current
Analog output therm. utilisation
Analog output PT 100 temperature.
Somewhere in the manual probably will be the answer, so hopefully someone may have had the pleasure.

regards

Phild

#2 GGOSS

GGOSS

    Senior Member

  • Moderator
  • PipPipPipPipPip
  • 407 posts
  • Location:Melbourne

Posted 08 December 2004 - 12:42 AM

Hello phild,

Don't waste your time going through the manual. Unfortunately, the analogue output on the CET4 is not scaleable. The fact that you know 12mA = 100% should allow to scale the PLC accordingly.

Hope the above helps.

Regards,
GGOSS