VFD Is tripping when command stop is given


  • Please log in to reply
2 replies to this topic

#1 Guest__*

Guest__*
  • Guests

Posted 16 January 2005 - 05:18 AM

Hi there, i need some input from you guys. I have this Siemens VFD installed in our plant. It drives a 11kw motor to rotate a Drum/cylinder. All of the time when i stopped it, the VFD gives an alarm of phase loss. I tried to measure the voltage while stopping but the voltage is present at all phase. I have tried to adjust the ramp down time but no success is obtained... Hope you can help me on this.. TNX

#2 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,602 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 16 January 2005 - 05:52 PM

Hi

I have come across this type of performance if the inertia of the drum is too high, or is unbalanced.
I would try to set the ramp down period to a long setting, or to set the stop mode to coast down.

Best regards,

#3 jraef

jraef

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 683 posts
  • Gender:Male
  • Location:USA, California

Posted 31 January 2005 - 05:04 PM

I would also make sure that you do not have a safety system which disconnects power every time you stop the drum.
"He's not dead, he's just pinin' for the fjords!"