An triphasic sistem feed an electric load; currents on each phase are differents. What kind of capacitor I must use to compensate reactive energy: triphasic one ( interior conection delta) or monophasic ( different value on each phase). Thank you!

unequal triphasic load
Started by adin62, Apr 10 2005 07:05 PM
1 reply to this topic
#1
Posted 10 April 2005 - 07:05 PM
#2
Posted 24 May 2005 - 12:13 AM
Hi
I expect that this must be a four wire system, i.e. a system using three phase plus neutral.
In this case, I would use single phase capacitors to correct each phase.
Best regards,
I expect that this must be a four wire system, i.e. a system using three phase plus neutral.
In this case, I would use single phase capacitors to correct each phase.
Best regards,