Posted 22 May 2005 - 12:24 PM

hello.......

i`m having a 3ph induction motor star connected with rated voltage = 380 v and rated frequency =50 hz ......
i`m trying to control its speed by keeping the supply volyage constant=380v and decreasing the applied frequency to= 30 hz

an engineer told me that i must also decrease the applied votlage by the ratio =380/50 so as to keep the flux constant , and to avoid the increase of the flux that may casue overheating to the motor .......

i just want to ask :how could the high flux in the air gap or in the iron core of the stator or the rotor could cause over heating on the induction motor

please answer me as quick as possible.....

thx

#2 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,642 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 22 May 2005 - 07:08 PM

Hello maxona

Welcome to the forum.

Increasing the flux in the iron has two affects.
1] increaseing the hysteresis losses in the iron. (heating the iron)
2] Changing the inductance.
As the flux in the iron increases, the inductance changes. Above a particular amount of flux, there is a reduction in inductance as the flux is increased.
The effect of the reduction in inductance for a voltage driven circuit, is that the impedance reduces resulting in more curent flow and more flux. This in turn further reduces the inductance, increases the flux and increases the hysteresis loss etc etc.....

Best regards,

#3 mazona

mazona

    Junior Member

  • Members
  • PipPip
  • 9 posts

Posted 23 May 2005 - 03:19 PM

hello...

thanx for fast response

i`d like to ask about the effect of the flux saturation in the iron core from the thermal point of view.

#4 marke

marke

    Posting Freak

  • Moderator
  • PipPipPipPipPipPip
  • 2,642 posts
  • Gender:Male
  • Location:Christchurch, New Zealand

Posted 23 May 2005 - 07:00 PM

Hello mazona

Saturation of the iron wil cause a significant increase in the iron loss of the motor. This will increase the heating of the iron and can lead to motor failure.

Typically, at rated load, the motor is designed such that the iron loss and copper loss are of the same order of magnitude. The copper loss is often in the order of 50% higher than the iron loss, but may be equal. If the iron loss is increased significantly, this will result in a significant increase in the total losses of the motor. For example, if the iron loss was doubled, the motor could over heat under open shaft (no load) conditions.

Best regards