Operational Parameters
parameter : function : Suggested start point
500 : Running Pressure : Dependent on transducer
321B : Pipe Fill Speed : 30 - 35 Hz
822 : Pipe Fill Pressure : About 10-20% running pressure
321A : Minimum speed : Set to keep pumping (30-40Hz)
322A : Maximum speed : 50Hz
28F : Sleep frequency : Equal to or greater than min speed (321A)
28G : Sleep Delay : 30 seconds
28H : Wakeup pressure : 50-90% of running pressure
817 : Broken Pipe Torque : 90 - 120%
819 : Dry Pump : Under torque 10 - 20%
Connections
Link : #10 to #20
Link : #21 to #22
Start : #8 to #11
Pressure Transducer : #3 (-ve) to #11 (+ve)
CODE
[b]Code: [/b]
Setup in this order:
212 = keyboard
213 = remote
214 = R
281 = ON
282 = 2
287 = 0%
288 = 98%
28F = 30Hz
28G = 30 seconds
28H = 30%
28I = Fall
441 = !A1
821 = ANIN2
822 = 10%
234 = A
311 = 10S
315 = 10S
321A = 30Hz
322A = 50Hz
343A = ON
416 = 4-20mA; Set link S$ on pcb to current
234 = B
321B = 30Hz
322B = 50Hz
343B = Invert
234 = Digin3
811 = Min+Max
812 = Max
815 = 2s
817 = Set to over torque trip point
819 = 10
81A = 0
823 = frequency
824 = 28
825 = min alarm
831 = CA2
832 = &
833 = CD1
834 = .
428 = Ext Trip
442 = !LY
Setup in this order:
212 = keyboard
213 = remote
214 = R
281 = ON
282 = 2
287 = 0%
288 = 98%
28F = 30Hz
28G = 30 seconds
28H = 30%
28I = Fall
441 = !A1
821 = ANIN2
822 = 10%
234 = A
311 = 10S
315 = 10S
321A = 30Hz
322A = 50Hz
343A = ON
416 = 4-20mA; Set link S$ on pcb to current
234 = B
321B = 30Hz
322B = 50Hz
343B = Invert
234 = Digin3
811 = Min+Max
812 = Max
815 = 2s
817 = Set to over torque trip point
819 = 10
81A = 0
823 = frequency
824 = 28
825 = min alarm
831 = CA2
832 = &
833 = CD1
834 = .
428 = Ext Trip
442 = !LY
Best regards,