In Topic: Do Power factor correction capacitors reduce Energy bill?

25 June 2010 - 11:50 AM

QUOTE (subhash @ Oct 17 2006, 12:27 AM) <{POST_SNAPBACK}>
Hallo Mark
1. Motor Load was constant through out experiment for both with and without capacitor in circuit .
that same motor is connected with constant flow pump application.
2. Without capacitor power factor was : 0.80 and with capacitor power factor is : 0.95
3. Regarding voltage drop it is seems to be nil as where capacitor added and power measure is seprated
by Y/D starter contactor only.
4.Before correction feeder line current was - R-48.0A Y-48.0A B-49.0A / After correction Current is -R-40A Y- 40A B-41.0A

Regards

Subhash

Hi subhash
you have done very good job, have you tried it on another motors
what is your experiance now?
is it really worth to connect the capacitors at motor ?