post Mar 29 2006, 12:52 PM
Post #1


Junior Member
**

Group: Members
Posts: 2
Joined: 29-March 06
Member No.: 1,444



Dear Sirs,
I have one question and I hope that you can help me! In My site I have 4 KV Motor with 650HP and 0.92 Power Factor, and I want to calculate the Kw/Day for the motor but I don’t have the formula to calculate KW/Day. And another question that is the power rating which is written on the name plate (650HP) is it the same (650 HP/Hr)? And if not, what is the formula to find the HP/Hr from the rated power on the name plate?

I Hope that you will answers my doubts.

Many Thanks,

Mohammad Tahseen
Go to the top of the page
 
+Quote Post
marke
post Mar 29 2006, 06:38 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,054
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Mohammad

The rated power of the motor (KW or HP) is the rated output power of that motor. When the motor is operating at full load, it should be producing that nameplate power out the motor shaft.
The electrical input power will be higher because it will also include the losses in the motor.
If we assume that the motor has an efficiency of say 92%, then the input power will be the output power divided by the efficiency.

In order to calculate the KW/Hr used by the motor, you need to know the power consumed by the motor and this is dependant on the shaft power that the motor is producing. In otherwords, it is very load dependant. There is no magic formula that will give you this information unless you know what the output power is.

If we assume that the motor operates continuously at rated shaft power, then the KWHrs used would be 650 x 0.746 KW / efficiency x number of hours run. Note this assumes continuous operation at full load. This is very rarely the case!! At half load, the KWHrs will be almost halved.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
Mohammad.tahseen
post Mar 30 2006, 06:15 AM
Post #3


Junior Member
**

Group: Members
Posts: 2
Joined: 29-March 06
Member No.: 1,444



Thank you very much for your replay, you cleared my doubts, but when I asked about the rated power is it the same Kw/Hr what I mean, if the motor runs at the full load for one hour, is the Kw/Hr reading will be the same (name plate rated power?, and from what I understood from your replay that the name plate power is the mechanical power and to find the input electrical power we have to divide by the efficiency.
So if I have continuous reading of the current as a feed back to PLC system and already my voltage is fixed to around 4.0KV and I Know the power factor, Can I take one calculation each one minute (or less) for the power (sqr3*I*V*P.F) for one hour and find the average and consider it as Kw/hr then multiply this with working hours for one day to find Kw/Day??

Many Thanks and Best Regards
Go to the top of the page
 
+Quote Post
marke
post Mar 30 2006, 10:11 AM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,054
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Mohammad

Yes, if you measure the input power, you can integrate this over the period of use to determine the KWHrs consumed.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 marke 2,269 19th August 2008 - 07:06 PM
Last post by: marke
No New Posts   0 marke 1,485 15th August 2004 - 12:13 AM
Last post by: marke
No New Posts   0 Tassio 1,911 21st November 2004 - 06:21 AM
Last post by: Tassio
No New Posts 4 rotormtr 894 17th January 2007 - 03:44 AM
Last post by: rotormtr
No New Posts 3 rahuljadhav1 749 29th October 2007 - 04:31 AM
Last post by: rahuljadhav1



RSS Lo-Fi Version Time is now: 22nd August 2008 - 12:44 AM
hosted by : L M Photonics Ltd