Oversized Motors, Common Misconception
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
marke
post Sep 11 2006, 01:49 AM
Post #1


Posting Freak
******

Group: Moderator
Posts: 2,031
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



I often see statements from "reputible" sources suggesting that the use of oversized motors causes energy to be wasted.
In many cases, this is not true, infact there can be an advantage in using an oversized motor.

For example, from a manufacturers data sheet (attached) I see the following:

11KW motor.
100% load 89.2% eff

15KW motor
75% load 89.7% eff

22KW motor
50% load 90.7% eff

So, if I have an 11KW load, I would be most efficient to use the 22KW motor at half load, followed by the 15KW motor at three quarter load and least efficient to use the 11KW motor at full load.
The oversized motors would run cooler, and therefore would last longer as well. The disadvantages of using an oversized motor would be that the start current will be higher and the capital cost is also higher.

I find the same if I compare the 30, 45 and 55KW motors, and others as well.

As I see it, the use of an oversized motor does not waste energy, it actually can save energy!!

Best regards,
Attached File(s)
Attached File  4_pole_motors.pdf ( 874.31K ) Number of downloads: 140
 


--------------------
Go to the top of the page
 
+Quote Post
GGOSS
post Sep 11 2006, 02:35 AM
Post #2


Senior Member
*****

Group: Moderator
Posts: 403
Joined: 17-May 02
From: Melbourne
Member No.: 14



I would tend to agree with most of that, however expect that you're comment regarding starting current would apply to DOL starting only. The amount of torque required to start the load would be the same irrespective of motor size, therefore it should be possible to start at the same level of current (actual amps) via for example a soft starter that allowed for start current adjustment in 1% FLC increments, in other words upper end soft starter products.

Regards,
GGOSS
Go to the top of the page
 
+Quote Post
marke
post Sep 11 2006, 03:03 AM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,031
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Now theres a trap!!

If we have a 11KW load and we need to have 50% start torque, then with the 11kw motor, we would have a start current Is to develp that torque.
If now we double the size of the motor, then the start torque relative to the motor is now 25%. The rated current is double the 11KW, but torque is proportional to current squared. If we had the same start current (Amps) then it would a lower start torque per amp and so we would have less start torque.
With the larger motor (twice the size, we will need a start current that is 41% higher than the 11KW motor (start current = rt2 times the start current)

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
GGOSS
post Sep 11 2006, 04:25 AM
Post #4


Senior Member
*****

Group: Moderator
Posts: 403
Joined: 17-May 02
From: Melbourne
Member No.: 14



You're absolutely correct. Don't know what I was thinking.

Maybe it's time to open that Fish 'n' Chip shop.

Regards,
GGOSS
Go to the top of the page
 
+Quote Post
mariomaggi
post Sep 11 2006, 06:21 AM
Post #5


Member
****

Group: Full Member
Posts: 197
Joined: 15-March 05
From: Milan, Italy
Member No.: 1,068



Dear marke,
you wrote some interesting considerations. But these considerations are related to standard motors with standard efficiency.
If you compare a standard efficiency motor with an high-efficiency motors (for example, Class Eff1 or Eff1+), you will see better results. In other words, if the motor is not so stressed by heat due to low quantity of copper used, and induction on magnet steel is normal and not too high, motor efficiency will be better. You can find the same conditions in a bigger motor at 50% of load.
Please note that using a bigger motor the power factor will decrease, and you will be obliged to make a compensation.
Furthermore, for frequently started motors, the higher inertia will be a further cost in energy for acceleration.

Regards
Mario


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   4 Itos 1,397 24th June 2002 - 04:02 AM
Last post by: Itos
No New Posts   1 Itos 1,264 26th June 2002 - 08:56 PM
Last post by: marke
No New Posts   8 marke 2,740 20th October 2004 - 06:56 PM
Last post by: marke
No New Posts   1 -ksvs29- 1,373 15th August 2002 - 09:22 PM
Last post by: marke
No New Posts   0 GGOSS 1,414 12th August 2002 - 08:28 AM
Last post by: GGOSS



RSS Lo-Fi Version Time is now: 24th July 2008 - 11:49 PM
hosted by : L M Photonics Ltd