Enery saving through Variable Speed Drives
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Madhura
post Oct 10 2002, 03:58 AM
Post #1



*

Group: Members
Posts: 1
Joined: 10-October 02
Member No.: 130



Hi,
I wanted to know whether an energy saving can be obtained by using a variable seep drive. The motor details are as follows.

10hp, 3-phase Induction motor
720 rpm, 50hz, rating AOM
volts 380/440, 16.1 FLAmps

This is a trough motor in a tea factory (ventilation). Continuous operation for 10-14 hours. Currently running at the full speed. about 5 hours can be run at half the rpm. What will be the percentage energy saving possible.

Is there a chaper way of acheiving speed variation in steps. In this case 4 levels between Full spped and half the spped will be more than enough. Continuous speed variation based on sensors is not needed.

Are 3-speed motors in the market?

regards,
madhura.

[Edited on 10/10/02 by Madhura]
Go to the top of the page
 
+Quote Post
kim
post Oct 10 2002, 04:59 PM
Post #2


Junior Member
**

Group: Members
Posts: 2
Joined: 10-October 02
Member No.: 133



Hai Madhura,

You can save with VSD but the cost could be too high and your investment return could take years and the normally give way before you get back what you invest.

Look for analog motor loss controller.
Go to the top of the page
 
+Quote Post
marke
post Oct 16 2002, 09:00 AM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,086
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Madhura

Yes, you can certainly save energy, if it is being wasted. If you have a fan applications as you describe, and at full speed it is circulating more air than is necessary, then slowing it down will reduce the work done, and therefore the energy consumed.
One point to remember however, is that while the fan is running at full speed, it is consuming more energy when used with a drive, than connected directly to the supply. The drive itself consumes energy, typical efficiencies are in the order of 95%, so there is an energy loss of up to 5% in the drive, plus in most drives, there is a very distorted current drawn from the supply resulting in a poor power factor, higher KVA demand than a corrected motor and higher supply losses due to the harmonic currents.
If the fan system is currently controlled by shutters or similar mechanical means to control the air flow, then the energy wasted is already reduced, reducing the potential savings from speed control.
This means of energy optimisation is being heavily promoted by drive companies and definitely will reduce wasted energy, but I believe that it is sometimes oversold.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
tom
post Nov 2 2002, 02:56 AM
Post #4


Junior Member
**

Group: Root Admin
Posts: 7
Joined: 24-August 02
Member No.: 66



Hi
I was recently asked this question. Anybody got any comments?

Can you inform me as to what will be the chances of Energy saving with 3 phase Induction motor coupled to Compressor and is driven by AC variable frequency drive.Pl note this is constant torque application.The frequency (speed) reduction could be to about 30 Hz against rated Frequency of 50 Hz.
regards
Anil Deshpande
;p;
Go to the top of the page
 
+Quote Post
theDOG
post Nov 4 2002, 06:35 AM
Post #5


Intermediate Member
***

Group: Members
Posts: 45
Joined: 1-May 02
From: Melbourne
Member No.: 7



tom;

What type of compressor is it? Not all compressors are constant torque. If it is a piston type, it is (more than likely) a variable torque load. Oil flooded and rotary compressors are generally constant torque. Piston compressors are usually rare above 15kW.

The VSD can be modelled as a power source ie. VA in = VA out. The VSD not only changes the frequency of the motor, but also the voltage (have you heard of the VVVF?). Therefore, as the voltage and frequency decrease at the motor, the input current will decrease proportionally (assuming the motor current remains the same~constant torque). This of course does not take into account the relatively constant magnetising current required by the motor, which requires an "offset" in the V/Hz ratio.

As marke states in an earlier post, don't rule out other losses associated with the VSD.
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 marke 1,397 22nd May 2003 - 02:42 AM
Last post by: GGOSS
No New Posts   8 marke 6,368 3rd November 2006 - 01:00 PM
Last post by: Tim
No New Posts   3 GGOSS 1,284 22nd May 2003 - 02:34 AM
Last post by: GGOSS
No New Posts   1 marke 2,009 2nd November 2006 - 03:23 AM
Last post by: AB2005
No New Posts   3 rup_loc 1,185 30th May 2005 - 07:32 PM
Last post by: Carl



RSS Lo-Fi Version Time is now: 7th October 2008 - 11:17 PM
hosted by : L M Photonics Ltd