Hi, is it possible to measure power factor on the single phase supply at any single power point ? I need to make a simple PF electronic circuit with capacitor to save energy on my house by 24 hours without worried about over compensated which may cost my electricity bill more. I use less energy at home during daytime and more on the night time but using single capacitor would sometime over compensated during day time since it is not regulated automatically. My house is 240V, single phase with 30A suppy, during day time using 6 A and nigth time using 15A. How many microfarad needed ???
Go to the top of the page
 
+Quote Post
marke
post Oct 21 2002, 07:45 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello kongkc

Why do you want to power factor correct your house?? In all house situations that I have come across, the power is charged for KWHrs only. Power factor correction will NOT reduce the KWHrs used and therefore will not produce a rduction in your electricity bill.
Power factor correction will only be of value to you if you pay a KVA or power factor penalty. These are usually only applied to industrial consumers.
You must measure the power factor at the same place as the metering. You can not measure the power factor at a single phase outlet. Once you know the power factor, and the the connected load, and the basis of the power factor penalty, you can then determine the best strategy for power factor correction.
Best regards,


--------------------
Go to the top of the page
 
+Quote Post
kongkc
post Oct 21 2002, 08:27 AM
Post #3


Junior Member
**

Group: Members
Posts: 3
Joined: 21-October 02
From: Malaysia
Member No.: 145



I am supprised since I have bought an energy saving device and install at our house and it is just consist of capacitor and surge protector only. Current draw from the networks is actually lower by 10-20%. Is it consider saving ? The charges based on kwhrs.

I am confuse whether this device is cheating ?:(
Go to the top of the page
 
+Quote Post
marke
post Oct 21 2002, 08:38 AM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello kongkc

If you have a power factor of less than unity, then adding capacitance to the supply will reduce the current drawn from the supply, but will not reduce the KW. The current you measure consists of two parts, a resistive current that creates KW and a reactive part that does nothing. If you power factor is close to unity, then the resitive current is the highest. The total current drawn, is the square root of the sum of the squares of the two currents. A poowr power factor is due to inductive current from motors, transformers and discharge lighting (flourescent lighting). Adding capacitance effectively neutralises the inductive current, so the sum of the squares reduces, but the resistive current (making KW) stays the same.
Power factor correction can reduce current draw, reduce losses in the electrical supply, but does not slow your meter down.
Best regards,


--------------------
Go to the top of the page
 
+Quote Post
kongkc
post Feb 28 2003, 06:26 PM
Post #5


Junior Member
**

Group: Members
Posts: 3
Joined: 21-October 02
From: Malaysia
Member No.: 145



Hi Mark, I have actually save quite a lot of energy bill from using the capacitor correction device for my house. I been told that our KWH meter is actually a disk type and measure based on current. Therefore, it saves me quite a lot of energy.
Now, My factory is having a bulk capacitor correction bank. Could I save more energy by installing individual capacitor at the induction motor by increase the PF and reduce the current drawn ? I have the central mail PF automatic bank already, will it works ?:D
Go to the top of the page
 
+Quote Post
marke
post Mar 2 2003, 09:52 AM
Post #6


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello kongkc

Well what can I say? in a regular domestic environment, you pay for KWHrs measured by a rotating disk KWHr meter that measures power, not current. In this situation, you will not save any appreciable power by the addition of power factor correction. If the metering is faulty, or measures current rather than KWHrs, then it is possible that you will get a saving, but in that situation, I would suggest that you are being over charged in the first place, and I personaly would be getting some check metering done to make sure.
In regards to your factory, the addition of static power factor correction will reduce the current drawn, and therefore will reduce the i2R losses in the cables between the switchboard and the motor. This loss should be very small. If it is significant, then your cables must be well undersized. - I would not expect to see any significant savings.
Best regards,


--------------------
Go to the top of the page
 
+Quote Post
Guest__*
post May 1 2004, 09:43 AM
Post #7





Guests






Surely, a domestic power meter measures the product of the current and the voltage. Therefore, a reduction in the current drawn from the supply (by whatever means) would result in a lower measured power.
Go to the top of the page
 
+Quote Post
marke
post May 1 2004, 09:49 AM
Post #8


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



The domestic power meter measures the KW consumed. If you have a power factor of 1.0, then yes this is the product of V x I, but if the power factor is less than 1, then it will be less.
The actual formula for KW is V x I x Cos(thi) where cos(thi) is the power factor.
If you use capacitors to improve the power factor, the current will drop, but the power factor will improve and the KW will stay the same.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
Guest__*
post May 4 2004, 01:29 PM
Post #9





Guests






In a residential application, if power factor correction is installed on mass, can it reduce the amount of generation required to supply these homes?
Go to the top of the page
 
+Quote Post
marke
post May 4 2004, 07:12 PM
Post #10


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Yes,
If the collective power factor is low, there will be higher losses in the transmission system than needed. Corection of the power factor in this case will reduce the electrical supply losses in the cables, lines and transformers. This will not affect the KWhr consumed by the homes, but will reduce the losses in getting the KW to the homes.
Generally, dommestic installations have a faily high power factor because most of the load is heat and light, although today there is an increase in airconditioning units that run for an extended period of time causing a lagging power factor, and electronic devices suchs as TV and computer that have switchmode power supplies causing a poor harmonic power factor.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
Guest__*
post May 27 2004, 07:44 AM
Post #11





Guests






Hi, i also install a so called energy saving device, or perhaps it is function like a voltage stabilizer...

well, i dun see my electricity bill is being reduced. but in fact, my bill increase quite a lot...

could someone explain to me ???...
Go to the top of the page
 
+Quote Post
Guest__*
post Jun 26 2004, 07:47 AM
Post #12





Guests






;a;
Go to the top of the page
 
+Quote Post
marke
post Jul 4 2004, 07:26 PM
Post #13


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



In many cases, these "energy saving" devices are either not applied correctly, or have no scientific justification. Sometimes referred to as snake oil!!
You need to be careful with this type of equipment.
The NASA type energy saver does work in the right envirmonment, very small lightly loaded motors running for a very long period of time.
Other "energy savers" are actually power factor correction and this will not "save" energy in a domestic environment.
Best regards,


--------------------
Go to the top of the page
 
+Quote Post
Guest__*
post Jul 17 2004, 01:32 PM
Post #14





Guests






This site is very informative, thanks Marke...i had a second thought of buying "energy saving device"...a very simple computation for domestic environment...current drawn of the system is inversely proportional to its power factor!

rgds

Moises
Go to the top of the page
 
+Quote Post
Guest__*
post Jul 21 2004, 06:15 AM
Post #15





Guests






;p; hi u may also use active power factor correction for pf.
Go to the top of the page
 
+Quote Post
toprange
post Aug 1 2004, 03:17 PM
Post #16


Junior Member
**

Group: Members
Posts: 8
Joined: 1-August 04
Member No.: 831



Saving kWhr is the secondary benefit by using static capacitor next to the individual load, as the current reduced from the load the energy meter also sense less current to run the disk slower. It is my opinion. Please correct.
Go to the top of the page
 
+Quote Post
toprange
post Aug 1 2004, 04:33 PM
Post #17


Junior Member
**

Group: Members
Posts: 8
Joined: 1-August 04
Member No.: 831



If you found the bill got increasing after installing a capacitor because you installed at a wrong location. You should installed at the load side but not the line side otherwise the capacitor still consumed power even u turned off the appliance at home. I am still believe installing capacitor can reduce the kWhr because the distribution loss will be reduced because of reduction in current. Of course for a domestic used, you will not see the significant result but in a factory, it is a different story, you will see reduction in both of kVA and kWhr.
Go to the top of the page
 
+Quote Post
marke
post Aug 1 2004, 07:05 PM
Post #18


Posting Freak
******

Group: Moderator
Posts: 2,118
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello toprange

A KWHr meter or the "energy meter" is sensitive to KW, not current. If you connect a capacitor only to the meter, you will measure amps, but not KW and the disk will not rotate.
The addition of a power factor correction capacitor neutralises the laging powerfactor caused by inductive loads. This reduces the current flow, but does not reduce the KW in the load. The reduced current flow will reduce the power loss in the cables upstream of the correction bank, but this should be very low anyway. If this loss is significant in a short run of cable, then the cable must be well undersized.

Adding the capaciotr will not make the disk run slower!!
Best regards,


--------------------
Go to the top of the page
 
+Quote Post
toprange
post Aug 4 2004, 11:07 AM
Post #19


Junior Member
**

Group: Members
Posts: 8
Joined: 1-August 04
Member No.: 831



If the "energy meter" is snesitive to kW, Please tell me the principle of disk turning to calculate the kWhr.
Also, for example, after installing a capacitor bank , the current dropped from 1000A to 900A in 380V, 3 phase system, What will you expect the difference in kVA and kWhr?Please giving the detail explanation and calculation is much appreciated . Thank you.
Go to the top of the page
 
+Quote Post
marke