sir
we have in our Motor control centre motors of various capacities running.The starters are of DOL type and type 2 coordinated.we dont have ground fault protection for each motors.
in case of a insulation failure in any of the motors the incoming feeder to the mcc trips and the whole section gets affected.The fuses in the motor feeder also fails but the incomer breaker motor control centre mcc trips very fast. how to isolate the faulty motor alone
ram
Go to the top of the page
 
+Quote Post
jraef
post Mar 18 2007, 06:43 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 632
Joined: 22-February 03
From: USA, California
Member No.: 285



You need to perform a system coordination study, a process by which an electrical engineer determines the proper fusing and breaker trip settings to ensure that a fault is interrupted at the lowest possible level.


--------------------
"He's not dead, he's just pinin' for the fjords!"
Go to the top of the page
 
+Quote Post
ram14375
post Mar 24 2007, 02:11 PM
Post #3


Intermediate Member
***

Group: Full Member
Posts: 41
Joined: 17-December 05
Member No.: 1,308



QUOTE(jraef @ Mar 18 2007, 12:13 PM) [snapback]5739[/snapback]

You need to perform a system coordination study, a process by which an electrical engineer determines the proper fusing and breaker trip settings to ensure that a fault is interrupted at the lowest possible level.


thanks sir
since we have different ratings of motor is it possible to corelate all the fuse ratings with the breaker.Also i understand that whenever there is problem in the motor(ground fault) the overload relay should trip the contactor . on the otherhand if there is problem in the cable leading to motor the fuse should blow and the breaker should trip and the contactor is not supposed to open. your comments
ram
Go to the top of the page
 
+Quote Post
jraef
post Mar 24 2007, 11:17 PM
Post #4


Posting Freak
******

Group: Moderator
Posts: 632
Joined: 22-February 03
From: USA, California
Member No.: 285



An overload relay is not designed to trip on a ground fault specifically. It might trip if the ground current exceeds the setting, but often times if the ground fault has high resistance or acring, the ground current will be too low to be picked up by the OL relay. The best method is to use a ground fault relay of some sort, or possibly use a solid state OL relay that includes residual ground fault protection. Some do, some do not. You need to check for sure.


--------------------
"He's not dead, he's just pinin' for the fjords!"
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 GGOSS 2,253 28th July 2003 - 05:46 AM
Last post by: GGOSS
No New Posts   0 marke 2,177 11th June 2002 - 10:32 PM
Last post by: marke
No New Posts   0 marke 1,743 11th June 2002 - 10:34 PM
Last post by: marke
No New Posts   0 marke 1,573 11th June 2002 - 10:42 PM
Last post by: marke
No New Posts   0 marke 1,751 12th June 2002 - 09:24 AM
Last post by: marke



RSS Lo-Fi Version Time is now: 3rd July 2008 - 11:15 PM
hosted by : L M Photonics Ltd