Hi

For any one using Modbus with the MSF, you need to use two stop bits and zero parity, or one stop bit and even parity on the modbus master. If you use even parity, do not forget to turn on the parity on the MSF.

The MSF default settings are two stop bits and no parity.
The stop bits can not be independently controlled on the MSF.

Parameter 113:
0 = no parity, two stop bits
1 = even parity one stop bit

Best regards,


--------------------