post Nov 28 2002, 06:04 AM
Post #1


Senior Member
*****

Group: Moderator
Posts: 404
Joined: 17-May 02
From: Melbourne
Member No.: 14



Hi All,

As it has been a long time since my last post or response, I thought I might ask a couple of questions that may generate some interest and on-going discussion. These relate to starter ratings presentied in the format described by IEC60947-4-2.

Consider the following example.

125A: AC53a: 3.5 - 10: 70 - 10

125A implies starter rating expressed in Amps

AC53a implies starter is suitable for driving a squirrel cage motor and that the amps rating is based on continuous (non-bypassed) operation.

3.5 - 10 implies a maximum starting current of 3.5 x starter amps for a period not exceeding 10 seconds.

70 - 10 implies an on-load factor of 70% and 10 starts per hour equally spaced.

My questions are as follows:

1. Assuming we are able to start the driven machine within 5 seconds at a starting current not exceeding 3.5 time the starter rating, can we achieve 20 starts per hour (equally spaced and at 70% on-load factor) without compromising starter service life?

2. An on load factor of 70% and 10 starts per hour equally spaced implies a period of 350 seconds between completion of 1 start (ramp) and commencement of the next. What is the affect on starter ratings if the soft stop function is enabled?

I look forward to your responses.

Regards,
GGOSS
Go to the top of the page
 
+Quote Post
GGOSS
post Aug 18 2003, 07:02 AM
Post #2


Senior Member
*****

Group: Moderator
Posts: 404
Joined: 17-May 02
From: Melbourne
Member No.: 14



Still looking for help on this one. Can anyone provide some clues?

regards,
GGOSS
Go to the top of the page
 
+Quote Post
schow
post Nov 12 2004, 07:03 AM
Post #3


Intermediate Member
***

Group: Full Member
Posts: 42
Joined: 18-July 03
From: Deutschland
Member No.: 419



Please can anyone tell me what are the requirements (sub-clauses) of IEC60947-4-2? How many items are they?

Cheers!
Go to the top of the page
 
+Quote Post
GGOSS
post Nov 12 2004, 07:16 AM
Post #4


Senior Member
*****

Group: Moderator
Posts: 404
Joined: 17-May 02
From: Melbourne
Member No.: 14



Hello Schow,

Breakdown of IEC 60947-4-2 is as follows;

IEC 60947 is the standard applicable to Low-voltage Switchgear & Controlgear.

Part 4 of that standard relates to contactors and motor-starters.

Section 2 relates to AC Semiconductor motor controllers and starters.

Hope this helps.

Regards,
GGOSS
Go to the top of the page
 
+Quote Post
schow
post Nov 13 2004, 04:25 AM
Post #5


Intermediate Member
***

Group: Full Member
Posts: 42
Joined: 18-July 03
From: Deutschland
Member No.: 419



Hi GGOSS,

Thanks for the info but I need details of all sub-clauses, eg. for AC Drive EMC test IEC-61800-3, there are a few tests such as ESD, THD, conducted and radiated immunity, surge etc....If I remember correctly, there are about 7 or 8 tests altogether but for IEC/EN60947-4-2, how many are there?

I tried to check from our local test lab and most of them do not know details about this test. Pls can you tell me what are they? I need to look for a lab who can conduct tests required for IEC/EN60947-4-2.

Cheers! ;c;
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   5 uhaykir 2,505 5th July 2002 - 09:08 AM
Last post by: marke
No New Posts   3 marke 2,778 24th January 2003 - 07:05 PM
Last post by: marke
No New Posts   3 FbJavier 2,641 22nd May 2003 - 07:32 AM
Last post by: GGOSS
No New Posts   5 milliamp 1,912 21st September 2002 - 02:33 AM
Last post by: marke
No New Posts   2 tom 2,493 29th August 2002 - 08:49 AM
Last post by: GGOSS



RSS Lo-Fi Version Time is now: 1st December 2008 - 07:48 PM
hosted by : L M Photonics Ltd