Close Transition Star Delta Sequence., A LITTLE BIT CONFUSE
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
AZHAM
post Jun 21 2007, 12:42 AM
Post #1


Junior Member
**

Group: Members
Posts: 4
Joined: 20-June 07
Member No.: 3,395




HI ALL

i have a little bit confuse of sequence of start delta closed transition. what i understand is closed transition is to prevent the current spiked when the transition between star and delta are not connected. i just new , so i have study the old electrical schematic what i see in old project of my company first of all.

star contacter closed same time with closed transition contacter
then star contacter open and closed transition contacter remain closed
the delta contacter closed with the closed transition contacter.
and run continuously.

is it right?

from azham
Penang,Malaysia smile.gif
Go to the top of the page
 
+Quote Post
marke
post Jun 21 2007, 01:07 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,097
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Azham

There are two types of star delta starter.
The simplest and most common form is the open transition star delta starter and comprises three contactors, a main contactor, a star contactor and a delta contactor. In operation, the main contactor and the star contactor close together effectively connecting the motor to the supply in a star configuration. After a period of time, the star contactor opens, then after a small delay, the delta contactor closes.
for more information, see http://www.lmphotonics.com/star_delta.htm
The open transition causes high current and torque transients.

The second type of star delta starter is the closed transition star delta starter. This starter has four contactors. - there is an auxiliary delta contactor with one resistors in series with each pole, connected across the delta contactor. In operation, the main contactor and star contactor close together. After a period of time, the auxiliary delta contactor closes, then the star contactor opens, then the delta contactor closes.
The net result is that current flows through the motor windings at all times. There is no interruption of current flow.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
AZHAM
post Jun 21 2007, 01:42 AM
Post #3


Junior Member
**

Group: Members
Posts: 4
Joined: 20-June 07
Member No.: 3,395



hi marke

thank you for your information, how about if i design sc (star contactor) , tc (closed transition contacter) ,
mc (main contacter), dc (delta contacter).


mc and sc closed together
after a time delay tc closed, once the tc closed,

at the same time, sc open by the n/c from tc
dc closed by the n/c from sc

is it still same?
Go to the top of the page
 
+Quote Post
marke
post Jun 21 2007, 02:07 AM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,097
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Azham

I am not sure what you are referring to with your contactor names as in your first post you seemed to be calling the main contactor a closed transition contactor.
Without knowing what you are calling the main contactor, and the closed transition contactor, and how these are connected, it is impossible to comment.
I think that we need to have a sketch of the connections before commenting.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   0 marke 1,580 16th August 2002 - 01:36 AM
Last post by: marke
No New Posts   2 tom 2,450 29th August 2002 - 08:49 AM
Last post by: GGOSS
No New Posts   1 tom 1,650 15th August 2003 - 04:00 PM
Last post by: merajdab
No New Posts   1 gjnj1 1,124 28th September 2002 - 01:32 AM
Last post by: marke
No New Posts   4 koi6456 1,513 11th November 2002 - 06:36 PM
Last post by: koi6456



RSS Lo-Fi Version Time is now: 21st November 2008 - 01:19 AM
hosted by : L M Photonics Ltd