Hi All,

Can anyone advise (in detail) the implications of running a 3-phase variable speed drive from a 2 -phase supply source.

Regards,
GGOSS
Go to the top of the page
 
+Quote Post
theDOG
post Dec 4 2002, 04:30 PM
Post #2


Intermediate Member
***

Group: Members
Posts: 45
Joined: 1-May 02
From: Melbourne
Member No.: 7



There are a few issues that must be looked at:
1. The current passing through the rectifier (diodes or SCR's) will be increased by root 3, in comparison to the three phase bridge.
2. You will have an increase in DC ripple voltage.
3. The average DC bus voltage will be reduced significantly.

Solutions:
1. De-rate the drive by 50% ie. if you have a 10 amp motor, use a 20 amp VSD (you really only need 17.3 amps, but better to be safe than sorry)
2. Add either a DC link choke, or extra bus capacitors. Extra capacitance is more suitable as this will also increase the bus voltage, where the choke will have a voltage drop. Some manufacturers sell an extra capacitor that connects to the external bus terminals.
3. Check to see if the VSD has a phase loss fault - if this can not be defeated, forget all of the above!!

I have done this many times.
Go to the top of the page
 
+Quote Post
marke
post Dec 5 2002, 08:48 AM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,060
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello GGOSS
QUOTE

Can anyone advise (in detail) the implications of running a 3-phase variable speed drive from a 2 -phase supply source.

Yes the rectifiers will carry motr current, the ripple voltage will be much higher and the ripple current into the capacitors will also be much higher. This will reduce the life expectancy of the rectifier and the capacitors.
The frequency of the ripple voltage with a three phase input is 300 Hz and with two phase, is 100Hz (assuming 50Hz supply) For the same time constant, you would need three times the capacitance when only two phases used.
Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   12 marke 5,522 29th January 2008 - 04:41 PM
Last post by: EMartist
No New Posts   0 marke 991 13th May 2002 - 09:37 AM
Last post by: marke
No New Posts   4 Itos 1,500 24th June 2002 - 04:02 AM
Last post by: Itos
No New Posts   1 Itos 1,349 26th June 2002 - 08:56 PM
Last post by: marke
No New Posts   3 andy 1,334 5th September 2003 - 11:55 PM
Last post by: Underling



RSS Lo-Fi Version Time is now: 29th August 2008 - 09:32 AM
hosted by : L M Photonics Ltd