If the starter trips occasionally on phase loss, determine if there is a genuine phase imbalance condition occurring intermittently, and if so, try to correct the situation.
If the problem can not be fixed, then you can desensitize the starter by increasing the setting in parameter 7.
Maximum sensitivity is at a setting of 1 and minimum sensitivity is at a setting of 10.

If the problem continues with a setting of 10, and there is no current imbalance, it is probable that there is a fault on the control pcb.

The control pcbs are identical for all EMX and EMX2 models and can be swapped between units without any reprogramming.
Swap the main control pcb between two starters and see if the problem moves.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
GGOSS
post Aug 23 2007, 06:52 AM
Post #2


Senior Member
*****

Group: Moderator
Posts: 404
Joined: 17-May 02
From: Melbourne
Member No.: 14



The EMX and EMX2 starters are a closed loop controlled current soft starters which utilize external ring type current transformers (CT's) for the purpose of current measurement.

In addition to the information presented by Marke, it is wise to confirm that there are no loose connections in the secondary CT cabling. Check the integrity of electronic components and solder joints on the PCB to which the CT terminal strip connects is also suggested.

It is my humble opinion that the above-mentioned checks be performed before altering the setting of function 7 or swapping PCB's.

Regards,
GGOSS
Go to the top of the page
 
+Quote Post
marke
post Aug 23 2007, 07:13 AM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,099
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Good points GGOSS
I always ask those questions, but forgot to add them to the list here.
I rarely find any issues with the CT wireing etc except where there is an external earth attached.

- DO NOT connect an external earth to the CT secondaries!

Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   4 Itos 1,944 24th June 2002 - 04:02 AM
Last post by: Itos
No New Posts   1 Itos 1,568 26th June 2002 - 08:56 PM
Last post by: marke
No New Posts   3 andy 1,470 5th September 2003 - 11:55 PM
Last post by: Underling
No New Posts   0 andy 1,455 20th September 2002 - 04:44 AM
Last post by: andy
No New Posts   0 andy 554 --
Last post by: andy



RSS Lo-Fi Version Time is now: 1st December 2008 - 07:04 PM
hosted by : L M Photonics Ltd