Fuse and Cable selection for PFC bank
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Guest_necr_*
post Dec 7 2002, 07:32 AM
Post #1





Guests






Hi there.

Recently our PFC bank cables got overloaded and eventually failed. The cables emanate from the 3.3Kv bus bars and terminate at the PFC yard via a duct. The specs of the PFC bank are as follows; Voltage=3.3Kv, PFC bank rating=2.8Mvar and it is required to correct the power factor to 0.85. The cables to the PFC yard are two 150mm^2 capable of carrying 720A. So what i want to know is if the cable are adequate for the task. Further more i wolud like to know how to calculate the rating of the fuses protecting correction capacitors.
Go to the top of the page
 
+Quote Post
marke
post Jan 17 2003, 07:44 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,099
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



hello necr

From the information that you have given, I would expect the current to be in the order of 490 amps in which case the cable you have used should be adequate, however that is base on sinusidal voltage. The presence of harmonics rapidly increases the current flowing into the capacitors and this will put extra stress on the capacitors, cables and fuses.

The capacitors will have a maximum continuous current rating, depending on the design of the capaciotrs and that would be typically 1.2N or 1.4N This data will be available from the manufacturer and is an allowance for an increased current due to harmonics etc. For fusing you should select a fuse that is less than the current rating of the cable and I wouls also suggest less than the overlaod rating of the capacitors as well. If you use fast fuses and switch large banks of capacitors regularly, this can lead to premature fuse failure so you may need to use slow acting fuses.

If you are haveing problems with the PFC being overloaded, that would tend to suggest a high level of harmonics present and the best way to reduce the effect of these harmonics on your capacitors is to add detuning reactors in series with the capacitors. This makes the impedance inductive above the tuned frequency of the capacitor and choke (typically around 180 Hz) and reduces the current due to the fifth harmonics and above.

Best regards


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   0 ashishl 1,098 23rd May 2003 - 11:15 AM
Last post by: ashishl
No New Posts   1 dip04051978 847 16th August 2003 - 10:29 PM
Last post by: marke
No New Posts   1 dip04051978 784 2nd February 2004 - 08:22 AM
Last post by: jraef
No New Posts   3 bobg 1,857 19th August 2007 - 01:41 AM
Last post by: marke
No New Posts   4 dip04051978 1,105 16th August 2005 - 11:57 PM
Last post by: -Anonymous-



RSS Lo-Fi Version Time is now: 1st December 2008 - 08:55 PM
hosted by : L M Photonics Ltd