I undertand that different reduced starters are constant voltage or constant impedence or constant current starters, but what I don't understand is how that affects the motors current and torque. Best I can figure is that a constant impedence starter means that if you reduce the voltage the current also reduces. I need to understand the same for all three type of starters.
|
|
|
|
Sep 19 2007, 07:56 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,099 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello TCE
Welcome to the forum. At any time during the start, the torque produced by the motor is a function of the full voltage torque at that speed, and the square of the current being used to start the motor. The motor has an impedance which is a function of the motor design and the speed of the rotor. If you reduce the voltage applied to the motor, you will reduce the current. (I = V/Z) If you apply a constant reduced voltage to the motor during start, you can easily calculate the start current and torque curves from the full voltage curves. Likewise, if you apply a constant current start to the motor, you can also calculate the start torque curves from the full voltage current and torque curves. With a constant current start, the terminal voltage, is a function of the start current and the motor impedance which rises as the motor increases in speed. If you apply a constant impedance starter, then the voltage at the motor terminals at any speed is going to be a function of your starter impedance and the motor impedance which is a function of motor speed. As the motor accelerates, the motor impedance increases, so the motor terminal voltage increases. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
5 | uhaykir | 2,505 | 5th July 2002 - 09:08 AM Last post by: marke |
|||
![]() |
3 | marke | 2,778 | 24th January 2003 - 07:05 PM Last post by: marke |
|||
![]() |
3 | FbJavier | 2,641 | 22nd May 2003 - 07:32 AM Last post by: GGOSS |
|||
![]() |
4 | GGOSS | 1,825 | 13th November 2004 - 04:25 AM Last post by: schow |
|||
![]() |
5 | milliamp | 1,912 | 21st September 2002 - 02:33 AM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 1st December 2008 - 10:26 PM |