Hi
I am building a 3 phase converter using a 15 kva transformer to generate the 3rd leg. I need some way to bring my transformer up with out a huge inrush of current blowing fuses. Can I use a soft-starter for this or are they designed exclusively for motor control. Thanks tdarden3k |
|
|
|
Oct 20 2007, 03:34 AM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,099 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello TDARDEN
Yes, you certainly can use a soft starter to control a transformer, cone it plenty of times, but it may depend on your circuit configuration and on the transformer configuration. If you use a three phase soft starter, it will probably expect the output to be balanced and three wire only. If you use a single phase soft starter and transformer, ensure that it is rated for the voltage. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Oct 20 2007, 02:25 PM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 3 Joined: 20-October 07 Member No.: 3,916 |
Marke
Thanks for the reply . I had ordered a couple and was hoping I had not wasted my money. It is a single phase configuration (230 volt ) US operation and I ordered 208-240 volt devices. Also since I have never worked with these devices, do they vary the voltage to the controlled device or vary/limit the current to the device. Are the manually adjustable ? Thanks |
|
|
|
Oct 20 2007, 07:49 PM
Post
#4
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,099 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
The soft starter uses phase controlled SCRs to vary the average voltage applied to the load. Some soft starters incorporate a current feedback loop so that they can limit the average current applied, but I have not seen this feature on single phase units.
Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
32 | marke | 13,744 | 28th March 2008 - 01:02 PM Last post by: lau |
|||
![]() |
5 | uhaykir | 2,505 | 5th July 2002 - 09:08 AM Last post by: marke |
|||
![]() |
3 | marke | 2,778 | 24th January 2003 - 07:05 PM Last post by: marke |
|||
![]() |
1 | marke | 2,356 | 14th July 2003 - 12:44 AM Last post by: GGOSS |
|||
![]() |
3 | -Ravisankar- | 2,138 | 28th June 2002 - 08:04 AM Last post by: GGOSS |
|||
|
Lo-Fi Version | Time is now: 1st December 2008 - 08:53 PM |