I have two single phase, 120V motors in parallel. One is a 3/4 hp(10.4A) and the other is a 1/4hp(4A). I need to know what size capacitor to put in parallel with them to help aid power factor. The cap will be controlled by a microprocessor. If anyone knows the size or formulas for calculating the size please let me know.
|
|
|
|
Nov 8 2007, 02:30 AM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,010 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
To determine the amount of correction to apply, you first need to determine the level of the magnetizing current.
If you run the motors open shaft, (No shaft load) then the current drawn will essentially be the magnetizing current. If you apply static correction, then the correction current should be 80% of the magnetizing current. If you apply bulk correction, then you can correct higher than that. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Nov 8 2007, 07:25 AM
Post
#3
|
|
|
Senior Member ![]() ![]() ![]() ![]() ![]() Group: Full Member Posts: 207 Joined: 21-October 06 Member No.: 2,159 |
The cap will be controlled by a microprocessor. Why you want to use microprocessor? According to your question, you want to connect capacitor at motor terminal (static correction) then there is no need of microprocessor. You calculate the capacitor as Marke replied. -------------------- "Don't assume any thing, always check/ask and clear yourself".
|
|
|
|
Nov 13 2007, 07:14 AM
Post
#4
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,010 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Once you determine the amount of reactive current that you need, you can calculate the impedance using ohms law.
Z = V/I When you have calculated the impedance, you can calculate the capacitance as z = 1/(wc) therefore C = 1/(2 x pi x F x Z) or you can multiply the volts time the amps, divide by 1000 to get the required KVAR. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
1 | -Billy- | 2,418 | 6th May 2002 - 10:22 PM Last post by: marke |
|||
![]() |
0 | Asad | 1,657 | 11th May 2002 - 03:24 AM Last post by: Asad |
|||
![]() |
60 | marke | 15,065 | 27th March 2008 - 05:44 AM Last post by: Macabenta |
|||
![]() |
2 | Itos | 1,681 | 13th August 2002 - 03:40 PM Last post by: nadeem1990pk |
|||
![]() |
4 | Itos | 1,319 | 24th June 2002 - 04:02 AM Last post by: Itos |
|||
|
Lo-Fi Version | Time is now: 3rd July 2008 - 11:15 PM |