Ac Machine Loading |
![]() ![]() |
Ac Machine Loading |
Dec 3 2007, 11:08 AM
Post
#1
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 14 Joined: 15-August 07 Member No.: 3,633 |
Kindly clarify what will happen if a40 kw induction motor runs with no load for asufficient time. What will be the effect on power factor.
2. What will happen if a 250 kva alternator is loded with 40 percent load . |
|
|
|
Dec 3 2007, 06:08 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,099 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello NCT
If you run a motor under no load conditions, it will draw the magnetizing current which is typically 20% - 50% of the current rating of the motor. This is an inductive current and will reduce the plant power factor. The motor will also draw a small amount of current for the iron loss and also the frictional loss. These losses are pretty small depending on the motor, but can range from around 30% for small motors to 3% for large motors. The magnetizing current is constant and is independent of the motor load. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Dec 4 2007, 04:12 PM
Post
#3
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 12 Joined: 19-August 07 Member No.: 3,649 |
Hello NCT,
If you run an induction motor on no load, it will draw more reactive power from grid which will weaken the supply system and of course your power factor will come down and ultimately you have to make excess electricity bill for the same consumption..since the EB bills are charged on KVA basis.. if your power factor is low, your KVA will raise.. KW/PF = KVA (Power factor denomination reduces and the KVA increase..) For the generator nothing will happen if you running the set with 40% load of course the efficiency and cost of generation will increase.. Pragathees... Kindly clarify what will happen if a40 kw induction motor runs with no load for asufficient time. What will be the effect on power factor. 2. What will happen if a 250 kva alternator is loded with 40 percent load . |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
1 | kamranparacha | 1,379 | 18th April 2004 - 10:10 AM Last post by: marke |
|||
![]() |
7 | bob | 820 | 30th August 2005 - 08:34 AM Last post by: bob |
|||
![]() |
5 | -Anonymous- | 1,303 | 27th October 2005 - 07:50 PM Last post by: marke |
|||
![]() |
5 | hkharmonic | 1,080 | 9th April 2006 - 03:08 AM Last post by: marke |
|||
![]() |
4 | AB2005 | 965 | 31st January 2007 - 02:16 AM Last post by: AB2005 |
|||
|
Lo-Fi Version | Time is now: 1st December 2008 - 11:18 PM |