Generator Loads And Power Factor |
![]() ![]() |
Generator Loads And Power Factor |
Dec 4 2007, 02:48 AM
Post
#1
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 2 Joined: 3-December 07 Member No.: 4,066 |
This is my first post and I can tell from reading the other posts that in regards to technical knowledge, I am far behind most people on this site...so please speak slowly.
Situation: Have generator that runs multiple conveyors as well as other asphalt machinery. Question: If we use custom made capacitors to correct the Power Factor in circuit with each motor running off the generator. Then at a later time add additional conveyors (motors), will this effect the Power Factor of the motors we previously optimized. Thanks, Luke |
|
|
|
Dec 4 2007, 04:48 AM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,010 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello LukeC
Welcome to the forum. There are two types of power factor, displacement power factor and distortion power factor. Typically, most people considering power factor, are concerned with displacement power factor only. Every motor has a component of the current drawn which is called the magnetizing current. This is a characteristic of that particular motor and varies between motors. The magnetizing current is constant and independent of load. The magnetizing current is an inductive current and would generally be between 20% and 50% of the motor rated current. When the motor operates open shaft, it is essentially the magnetizing current that is drawn. Power factor correction capacitors are applied to the circuit to cancel out the inductive magnetizing current of the motor. If you add the correct amount of correction, then the power factor would typically be greater than 0.95. If you then add additional motors, the total magnetizing current will be increased and so the capacitor current needs to be increased also to give good correction. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
1 | -Billy- | 2,418 | 6th May 2002 - 10:22 PM Last post by: marke |
|||
![]() |
0 | Asad | 1,657 | 11th May 2002 - 03:24 AM Last post by: Asad |
|||
![]() |
60 | marke | 15,065 | 27th March 2008 - 05:44 AM Last post by: Macabenta |
|||
![]() |
2 | Itos | 1,681 | 13th August 2002 - 03:40 PM Last post by: nadeem1990pk |
|||
![]() |
4 | Itos | 1,319 | 24th June 2002 - 04:02 AM Last post by: Itos |
|||
|
Lo-Fi Version | Time is now: 3rd July 2008 - 11:15 PM |