Dear All
It is said that out put of CT must not float. Its winding may burn if float. Is it true? If yes then why the winding of general purpose distribution transformer not burn if there is no load at its secondary side? -------------------- "Don't assume any thing, always check/ask and clear yourself".
|
|
|
|
Dec 8 2007, 03:56 AM
Post
#2
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 187 Joined: 16-August 05 Member No.: 1,186 |
Hi AB2005,
The secondary side of a current transformer should rather never be left opened on the load side as dangerously high voltage will dvelop across the secondary winding and this could damage the CT. I hope this answer your question. Regards. Bob |
|
|
|
Dec 8 2007, 04:22 AM
Post
#3
|
|
|
Senior Member ![]() ![]() ![]() ![]() ![]() Group: Full Member Posts: 221 Joined: 21-October 06 Member No.: 2,159 |
The secondary side of a current transformer should rather never be left opened on the load side as dangerously high voltage will dvelop across the secondary winding and this could damage the CT. I hope this answer your question. Hello Bob I know about this. Read my Question carefully. -------------------- "Don't assume any thing, always check/ask and clear yourself".
|
|
|
|
Dec 24 2007, 09:44 AM
Post
#4
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 3 Joined: 9-November 07 Member No.: 3,988 |
Dear All It is said that out put of CT must not float. Its winding may burn if float. Is it true? If yes then why the winding of general purpose distribution transformer not burn if there is no load at its secondary side? Hi AB2005, The primary winding of a CT often operates at a high voltage with respect to earth. The secondary winding is usually designed to operate at a fairly low voltage with respect to earth. If you allow the secondary winding to float, the capacitance between the primary and secondary windings may cause a high voltage to be transferred to the secondary winding. It is possible for a flashover to occur (depending on the CT and the situation). CT secondary windings should ALWAYS be earthed to protect humans and secondary equipment from high voltages. Note that the same effect can occur in distribution transformers. Every winding should be earthed somewhere. The secondary windings of unloaded distribution transformers are usually earthed - often at the starpoint. Thanks, submonkey |
|
|
|
Apr 12 2008, 04:12 PM
Post
#5
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 16 Joined: 20-August 06 Member No.: 1,814 |
Dear all,
This is not to answer the ongoing discussion, but to put forward a issue, that there are several meters, like ammeters etc, require that the CT connection is to be done in such a manner that all S2 terminals are to be shorted (star) and grounded and a common earth wire to go to meter. While I have also come across several load managers and multifunction meters where it is required that all CT terminals (6 wires) must go directly to meter and then only the connection is correct and reading is also correct. Why these two different connections are required? Thanks |
|
|
|
Apr 13 2008, 09:37 AM
Post
#6
|
|
![]() Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 165 Joined: 3-September 04 Member No.: 861 |
Dear All It is said that out put of CT must not float. Its winding may burn if float. Is it true? If yes then why the winding of general purpose distribution transformer not burn if there is no load at its secondary side? See the difference in the turn ratio of a CT and a normal distribution transformer.....moreover the impedance comes into play ..the secondary of a current transformer when disconnected from its load while current is flowing in the primary will mean transformer secondary to continue driving current across the effectively infinite impedance This will produce a very high voltage across the open secondary (into the range of several kilovolts in some cases). Cheers. |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
1 | -shahbaz ali- | 2,160 | 28th August 2002 - 09:32 AM Last post by: marke |
|||
![]() |
0 | -shahbaz ali- | 1,320 | -- Last post by: shahbaz ali |
|||
![]() |
10 | theDOG | 1,731 | 25th September 2002 - 10:39 AM Last post by: marke |
|||
![]() |
11 | Alnerthyrn | 2,221 | 29th March 2005 - 02:44 AM Last post by: jraef |
|||
![]() |
1 | tom | 1,689 | 15th August 2003 - 04:00 PM Last post by: merajdab |
|||
|
Lo-Fi Version | Time is now: 1st December 2008 - 10:00 PM |