Current Transformer
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
AB2005
post Dec 7 2007, 05:40 AM
Post #1


Senior Member
*****

Group: Full Member
Posts: 221
Joined: 21-October 06
Member No.: 2,159



Dear All

It is said that out put of CT must not float. Its winding may burn if float. Is it true? If yes then why the winding of general purpose distribution transformer not burn if there is no load at its secondary side?


--------------------
"Don't assume any thing, always check/ask and clear yourself".
Go to the top of the page
 
+Quote Post
bob
post Dec 8 2007, 03:56 AM
Post #2


Member
****

Group: Full Member
Posts: 187
Joined: 16-August 05
Member No.: 1,186



Hi AB2005,

The secondary side of a current transformer should rather never be left opened on the load side as dangerously high voltage will dvelop across the secondary winding and this could damage the CT.
I hope this answer your question.

Regards.

Bob
Go to the top of the page
 
+Quote Post
AB2005
post Dec 8 2007, 04:22 AM
Post #3


Senior Member
*****

Group: Full Member
Posts: 221
Joined: 21-October 06
Member No.: 2,159



QUOTE (bob @ Dec 8 2007, 08:56 AM) *
The secondary side of a current transformer should rather never be left opened on the load side as dangerously high voltage will dvelop across the secondary winding and this could damage the CT.
I hope this answer your question.

Hello Bob

I know about this. Read my Question carefully.


--------------------
"Don't assume any thing, always check/ask and clear yourself".
Go to the top of the page
 
+Quote Post
submonkey
post Dec 24 2007, 09:44 AM
Post #4


Junior Member
**

Group: Members
Posts: 3
Joined: 9-November 07
Member No.: 3,988



QUOTE (AB2005 @ Dec 7 2007, 04:40 PM) *
Dear All

It is said that out put of CT must not float. Its winding may burn if float. Is it true? If yes then why the winding of general purpose distribution transformer not burn if there is no load at its secondary side?


Hi AB2005,

The primary winding of a CT often operates at a high voltage with respect
to earth. The secondary winding is usually designed to operate at a fairly
low voltage with respect to earth.

If you allow the secondary winding to float, the capacitance between the
primary and secondary windings may cause a high voltage to be
transferred to the secondary winding. It is possible for a flashover
to occur (depending on the CT and the situation).

CT secondary windings should ALWAYS be earthed to protect humans
and secondary equipment from high voltages.

Note that the same effect can occur in distribution transformers. Every
winding should be earthed somewhere. The secondary windings of
unloaded distribution transformers are usually earthed - often at the
starpoint.

Thanks,
submonkey


Go to the top of the page
 
+Quote Post
asif
post Apr 12 2008, 04:12 PM
Post #5


Intermediate Member
***

Group: Full Member
Posts: 16
Joined: 20-August 06
Member No.: 1,814



Dear all,

This is not to answer the ongoing discussion, but to put forward a issue, that there are several meters, like ammeters etc, require that the CT connection is to be done in such a manner that all S2 terminals are to be shorted (star) and grounded and a common earth wire to go to meter.

While I have also come across several load managers and multifunction meters where it is required that all CT terminals (6 wires) must go directly to meter and then only the connection is correct and reading is also correct.

Why these two different connections are required?


Thanks
Go to the top of the page
 
+Quote Post
chaterpilar
post Apr 13 2008, 09:37 AM
Post #6


Member
****

Group: Full Member
Posts: 165
Joined: 3-September 04
Member No.: 861



QUOTE (AB2005 @ Dec 7 2007, 08:40 AM) *
Dear All

It is said that out put of CT must not float. Its winding may burn if float. Is it true? If yes then why the winding of general purpose distribution transformer not burn if there is no load at its secondary side?



See the difference in the turn ratio of a CT and a normal distribution transformer.....moreover the impedance comes into play ..the secondary of a current transformer when disconnected from its load while current is flowing in the primary will mean transformer secondary to continue driving current across the effectively infinite impedance

This will produce a very high voltage across the open secondary (into the range of several kilovolts in some cases).

Cheers.
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   1 -shahbaz ali- 2,160 28th August 2002 - 09:32 AM
Last post by: marke
No New Posts   0 -shahbaz ali- 1,320 --
Last post by: shahbaz ali
No New Posts   10 theDOG 1,731 25th September 2002 - 10:39 AM
Last post by: marke
No New Posts   11 Alnerthyrn 2,221 29th March 2005 - 02:44 AM
Last post by: jraef
No New Posts   1 tom 1,689 15th August 2003 - 04:00 PM
Last post by: merajdab



RSS Lo-Fi Version Time is now: 1st December 2008 - 10:00 PM
hosted by : L M Photonics Ltd