Hi,
I hve got one 1,0 MW 11 kv slip ring motor which is designed for star connection at 11 k V . However, the supply voltage on my site is only 5,5 k V. I have two options 1. Star connected the motor at 5,5 k V which means that i will only have around 300 k W output shaft power. or 2. Delta connected the motor at 5,5 k V where I shall have somewhat slightly less than 1,0 mW output shaft power because of the derated voltage, 5,5 k V instaed of 6,35 kV across each winding. I need only around 600 k W for my application. Am i following the right path. Bob |
|
|
|
Dec 11 2007, 07:15 AM
Post
#2
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 12 Joined: 16-September 07 Member No.: 3,794 |
Dear Bob, You are definitely following right path 1.Out put Kw is propotional to square of voltage.So when you apply only 5.5Kv you get 25% of 1MW that is 250KW 2. If you connect the motor in delta and apply 5.5 kV you get 3 times more out put namely 750KW At the same time you have to take care of rotor volts which will be 50% in first case and 86% in second case while deciding starting resistances in rotor circuit subrao Hi,
hve got one 1,0 MW 11 kv slip ring motor which is designed for star connection at 11 k V . However, the supply voltage on my site is only 5,5 k V. I have two options 1. Star connected the motor at 5,5 k V which means that i will only have around 300 k W output shaft power. or 2. Delta connected the motor at 5,5 k V where I shall have somewhat slightly less than 1,0 mW output shaft power because of the derated voltage, 5,5 k V instaed of 6,35 kV across each winding. I need only around 600 k W for my application. Am i following the right path. Bob |
|
|
|
Dec 11 2007, 09:29 AM
Post
#3
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,054 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hi Bob
I agree with Subrao. Good information, and the note on the rotor is certainly one to watch out for. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Dec 13 2007, 03:45 AM
Post
#4
|
|
|
Member ![]() ![]() ![]() ![]() Group: Full Member Posts: 177 Joined: 16-August 05 Member No.: 1,186 |
Hello Marke,
Torque is proportionl to the square of the voltage but does it hold true for power also ? Regards. Bob |
|
|
|
Dec 13 2007, 05:09 AM
Post
#5
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,054 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Bob
Power equals Torque times Speed times a constant, so at a constant speed, the power is directly proportional to the speed. So yes, at a given speed, power is proportional to the square of the voltage. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
0 | Asad | 1,817 | 11th May 2002 - 03:24 AM Last post by: Asad |
|||
![]() |
3 | GGOSS | 1,231 | 22nd May 2003 - 02:34 AM Last post by: GGOSS |
|||
![]() |
5 | magdy El Kady | 1,365 | 26th September 2002 - 10:10 AM Last post by: GGOSS |
|||
![]() |
3 | jackson8000 | 1,106 | 20th January 2003 - 09:12 AM Last post by: marke |
|||
![]() |
0 | derf | 693 | 12th February 2003 - 10:50 PM Last post by: derf |
|||
|
Lo-Fi Version | Time is now: 22nd August 2008 - 12:42 AM |