Hi, i want to make a test bank to "test" generators. If i want to get 500kva from a 380 Volt gen, am i correct if i say:

I = 500.000/(1.73*380), then I=760Amps, each phase.

So, to use a star bank, R=220/760? R=0,29 ohms?

Can any one help me?

Thanks.

Chris.

Go to the top of the page
 
+Quote Post
chris1373
post Jan 24 2008, 03:18 AM
Post #2


Intermediate Member
***

Group: Full Member
Posts: 31
Joined: 6-September 06
Member No.: 1,906



Guys, can any one help me? Please!

I have a lot of iron and cantal res, but i want to know if they will work for the purpose.

Please, help me my friends!!!!!

Chris! tongue.gif
Go to the top of the page
 
+Quote Post
marke
post Jan 26 2008, 09:20 AM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,099
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Chris

Yes, that looks pretty good to me for a star connected load.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
chris1373
post Jan 28 2008, 01:48 PM
Post #4


Intermediate Member
***

Group: Full Member
Posts: 31
Joined: 6-September 06
Member No.: 1,906



Marke, can you tell me or were to look the amps per mm^2 that stainless steel can handle? The resistors that i have seems to be made of stainless steel!

Thanks in advance!

Chris.
Go to the top of the page
 
+Quote Post
chris1373
post Feb 6 2008, 01:42 AM
Post #5


Intermediate Member
***

Group: Full Member
Posts: 31
Joined: 6-September 06
Member No.: 1,906



I know that Marke do his best, so, can any one else help me please?

Chris!

QUOTE (chris1373 @ Jan 28 2008, 02:48 PM) *
Marke, can you tell me or were to look the amps per mm^2 that stainless steel can handle? The resistors that i have seems to be made of stainless steel!

Thanks in advance!

Chris.

Go to the top of the page
 
+Quote Post
marke
post Feb 6 2008, 05:54 AM
Post #6


Posting Freak
******

Group: Moderator
Posts: 2,099
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Chris

Unfortunately, it is not as just a figure of Amps per square mm.
You are looking for an intermittant rating. There is power dissipated in the resistors due to the current through them and their resistance. This power will cause a temperature rise that is dependent on the power dissipated and the thermal resistance of the resistors.
The thermal resistance is a function of the total surface area of the resistors and the air flow through them. For short term overloads, you really need to know the transient thermal resistance for different time periods so that you can use the appropriate thermal resistance for the duration of the overload only.

You also need to know the maximum operating temperature that is acceptable in your installation.

Note, different grades of stainless steel will have different resistances.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
chris1373
post Feb 7 2008, 02:36 AM
Post #7


Intermediate Member
***

Group: Full Member
Posts: 31
Joined: 6-September 06
Member No.: 1,906



Marke, i only need to know the minimum amps that my resistors can handle, not anything else!

I can send you pictures of the the resistor if it helps!

Please, give me a hand!

Chris.

PS: Is there any table you know for the current rating that stainless steel can handle, an aprox will do it?

QUOTE (marke @ Feb 6 2008, 05:54 AM) *
Hello Chris

Unfortunately, it is not as just a figure of Amps per square mm.
You are looking for an intermittant rating. There is power dissipated in the resistors due to the current through them and their resistance. This power will cause a temperature rise that is dependent on the power dissipated and the thermal resistance of the resistors.
The thermal resistance is a function of the total surface area of the resistors and the air flow through them. For short term overloads, you really need to know the transient thermal resistance for different time periods so that you can use the appropriate thermal resistance for the duration of the overload only.

You also need to know the maximum operating temperature that is acceptable in your installation.

Note, different grades of stainless steel will have different resistances.

Best regards,

Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No new   14 GGOSS 1,568 28th January 2003 - 04:08 PM
Last post by: gwosun
No New Posts   2 FbJavier 1,370 21st September 2003 - 11:18 PM
Last post by: electricpete
No New Posts   3 andy 1,470 5th September 2003 - 11:55 PM
Last post by: Underling
No New Posts   0 andy 1,455 20th September 2002 - 04:44 AM
Last post by: andy
No New Posts   0 andy 554 --
Last post by: andy



RSS Lo-Fi Version Time is now: 1st December 2008 - 11:23 PM
hosted by : L M Photonics Ltd