Analytical Or Field Studies Of Pf Correction Energy Savings, How much can line losses be reduced in C&I facilities?
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
Dan_G
post Feb 5 2008, 12:04 AM
Post #1


Junior Member
**

Group: Full Member
Posts: 6
Joined: 11-December 06
Member No.: 2,698



This forum has quite an extensive history discussing power factor correction related topics. I read many posts regarding energy savings, and found in several of them the statement that there are no energy savings whatsoever. I've seen lots of claims from unscrupulous vendors out there claiming extraordinary energy savings of 20% or more, but the fact remains that there are non-zero savings because when pf is corrected, less current flows, and I2R losses are reduced in transformers, conductors, etc. I have been told by several PQ experts that such energy savings will usually be below 1% of consumption in commercial and industrial facilities, but that in rare instances savings could amount to as much as 3% of consumption.

I have tried several times to find studies that document these small energy savings from pf correction, but so far, all I've been able to find is anecdotal. I'd really like to have a report based on a field study or maybe a theoretical study using a model of a typical electrical distribution system of a C&I facility. Such evidence would provide a firm foundation for combatting inaccurate energy savings claims. Does anyone know of any studies that could help?

Go to the top of the page
 
+Quote Post
marke
post Feb 5 2008, 09:34 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,031
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello Dan_G

The addition of power factor correction does save energy, there is no dispute about that, but it will not reduce the energy consumed by equipment connected to the supply. The energy saved is in the distribution equipment on the supply side of the power factor correction equipment.

If you apply power factor correction to your main switchboard, you will not see any savings on your supply meter unless there is a long cable between your meter and your main board.

Some sales people claim that energy (KWHrs) will be reduced significantly in the corrected plant and this is not true. The energy savings are in the distribution system and that is not metered at the consumers plant. Cost savings are based on power factor or KVA penalties.

In the distribution system, the addition of power factor correction not only reduces i2r losses in the cables and transformers, but it increases the utilization of transformer and generators. The transformer and alternator loading is based on current. (often expressed as KVA) If you have a load power factor of 0.5, the maximum KW loading on a transformer is halved. Correcting the power factor up to 1.0 would enable two time the KW loading on a transformer compared to it's maximum load at a power factor of 0.5 - This saves a lot of investment in distribution plant.

I do not have any case studies covering the savings in the distribution system, but it is easy to calculate what savings can be made provided that you know what the losses are.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
Dan_G
post Feb 6 2008, 12:03 AM
Post #3


Junior Member
**

Group: Full Member
Posts: 6
Joined: 11-December 06
Member No.: 2,698



Thanks Mark. I agree with everything you wrote, but it would still be helpful to have some empirical data to show to people who are accosted by PF correction savings peddlers.
Go to the top of the page
 
+Quote Post
jraef
post Feb 7 2008, 03:42 AM
Post #4


Posting Freak
******

Group: Moderator
Posts: 636
Joined: 22-February 03
From: USA, California
Member No.: 285



Here is a study that implies it.
Look at table 2 on page 3. It shows that they implemented a $55,000.00 power factor improvement program, but list the energy savings as "N/A", meaning there was none. They do show cost savings and payback because they avoided a lot of penalties, but that had nothing to do with energy savings.

http://www1.eere.energy.gov/industry/bestp...rld_alumina.pdf

By the way, here is the results of my search at this site, there are some other interesting reads there.

http://search.nrel.gov/query.html?qp=url%3...amp;x=0&y=0


--------------------
"He's not dead, he's just pinin' for the fjords!"
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
2 User(s) are reading this topic (2 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 marke 1,278 22nd May 2003 - 02:42 AM
Last post by: GGOSS
No New Posts   0 marke 1,663 11th June 2002 - 10:42 PM
Last post by: marke
No New Posts   1 Itos 1,264 26th June 2002 - 08:56 PM
Last post by: marke
No New Posts   1 marke 1,899 2nd November 2006 - 03:23 AM
Last post by: AB2005
No new   17 marke 3,774 4th August 2005 - 07:10 PM
Last post by: marke



RSS Lo-Fi Version Time is now: 24th July 2008 - 11:48 PM
hosted by : L M Photonics Ltd