Star-delta Contactors Rating?
Digg this topic · Save to del.icio.us · Slashdot It · Post to Technorati · Post to Furl · Submit to Reddit · Share on Facebook · Fark It · Googlize This Post · Add to ma.gnolia · Tag to Wink · Add to MyWeb · Add to Netscape
chris1373
post Feb 6 2008, 01:38 AM
Post #1


Intermediate Member
***

Group: Full Member
Posts: 31
Joined: 6-September 06
Member No.: 1,906



I have to put together a star delta starter, for a 150 HP motor, it will start without load!

What will be the KW contactors you will pick?

I am not sure if i use new ones ore used ones!

If i use new, will they be for 132KW enought? If i use some siemens used ones, but in very good condition, shoul they be biger in KW?

Thanks for your answers!!!

Chris!
Go to the top of the page
 
+Quote Post
marke
post Feb 6 2008, 05:40 AM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,099
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hi Chris

The star contactor should be rated at 1/3 of the motor rating, i.e. DOL rated for 50HP and the other two contactors should be rated at 58% of the motor rating provided that both are connected to the input lines. If the input three phase is connected to the main contactor only, and the delta contactor is taken from the output of the main contactor, then the main contactor is carrying the full line current and should be rated at 150HP.

Note: the star and the delta contactor must be mechanically and electrically interlocked and a special star delta timer must be used. There must be a small delay between the star contactor opening and the delta contactor closing to allow the arc to extinguish.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post
chris1373
post Feb 12 2008, 01:29 PM
Post #3


Intermediate Member
***

Group: Full Member
Posts: 31
Joined: 6-September 06
Member No.: 1,906



What will be the use of the line contactor if i conect the delta contactor from the output of the line contactor?

Chris.

PS: Is there any abbreviation for "contactor"? biggrin.gif

QUOTE (marke @ Feb 6 2008, 06:40 AM) *
Hi Chris

The star contactor should be rated at 1/3 of the motor rating, i.e. DOL rated for 50HP and the other two contactors should be rated at 58% of the motor rating provided that both are connected to the input lines. If the input three phase is connected to the main contactor only, and the delta contactor is taken from the output of the main contactor, then the main contactor is carrying the full line current and should be rated at 150HP.

Note: the star and the delta contactor must be mechanically and electrically interlocked and a special star delta timer must be used. There must be a small delay between the star contactor opening and the delta contactor closing to allow the arc to extinguish.

Best regards,

Go to the top of the page
 
+Quote Post
marke
post Feb 14 2008, 11:18 AM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,099
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



The common connection of a star delta starter connects the incoming supply to the input of both the main and the delta contactors.
This configuration minimises the size of the contactors, but requires two contactors to be opened to disconnect the motor for the supply.
If the delta contactor is connected to the output of the main contactor, the size of the main contactor must be increased to the DOL rating for the motor, and only the main contactor needs to be opened to disconnect the motor from the supply.

Best regards,


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 tom 2,496 29th August 2002 - 08:49 AM
Last post by: GGOSS
No New Posts   1 gjnj1 1,152 28th September 2002 - 01:32 AM
Last post by: marke
No New Posts   4 koi6456 1,530 11th November 2002 - 06:36 PM
Last post by: koi6456
No New Posts   0 markfoley 1,027 26th February 2003 - 12:36 PM
Last post by: markfoley
No New Posts   1 dip04051978 847 16th August 2003 - 10:29 PM
Last post by: marke



RSS Lo-Fi Version Time is now: 1st December 2008 - 11:00 PM
hosted by : L M Photonics Ltd