I have to put together a star delta starter, for a 150 HP motor, it will start without load!
What will be the KW contactors you will pick? I am not sure if i use new ones ore used ones! If i use new, will they be for 132KW enought? If i use some siemens used ones, but in very good condition, shoul they be biger in KW? Thanks for your answers!!! Chris! |
|
|
|
Feb 6 2008, 05:40 AM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,099 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hi Chris
The star contactor should be rated at 1/3 of the motor rating, i.e. DOL rated for 50HP and the other two contactors should be rated at 58% of the motor rating provided that both are connected to the input lines. If the input three phase is connected to the main contactor only, and the delta contactor is taken from the output of the main contactor, then the main contactor is carrying the full line current and should be rated at 150HP. Note: the star and the delta contactor must be mechanically and electrically interlocked and a special star delta timer must be used. There must be a small delay between the star contactor opening and the delta contactor closing to allow the arc to extinguish. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Feb 12 2008, 01:29 PM
Post
#3
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 31 Joined: 6-September 06 Member No.: 1,906 |
What will be the use of the line contactor if i conect the delta contactor from the output of the line contactor?
Chris. PS: Is there any abbreviation for "contactor"? Hi Chris The star contactor should be rated at 1/3 of the motor rating, i.e. DOL rated for 50HP and the other two contactors should be rated at 58% of the motor rating provided that both are connected to the input lines. If the input three phase is connected to the main contactor only, and the delta contactor is taken from the output of the main contactor, then the main contactor is carrying the full line current and should be rated at 150HP. Note: the star and the delta contactor must be mechanically and electrically interlocked and a special star delta timer must be used. There must be a small delay between the star contactor opening and the delta contactor closing to allow the arc to extinguish. Best regards, |
|
|
|
Feb 14 2008, 11:18 AM
Post
#4
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,099 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
The common connection of a star delta starter connects the incoming supply to the input of both the main and the delta contactors.
This configuration minimises the size of the contactors, but requires two contactors to be opened to disconnect the motor for the supply. If the delta contactor is connected to the output of the main contactor, the size of the main contactor must be increased to the DOL rating for the motor, and only the main contactor needs to be opened to disconnect the motor from the supply. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
2 | tom | 2,496 | 29th August 2002 - 08:49 AM Last post by: GGOSS |
|||
![]() |
1 | gjnj1 | 1,152 | 28th September 2002 - 01:32 AM Last post by: marke |
|||
![]() |
4 | koi6456 | 1,530 | 11th November 2002 - 06:36 PM Last post by: koi6456 |
|||
![]() |
0 | markfoley | 1,027 | 26th February 2003 - 12:36 PM Last post by: markfoley |
|||
![]() |
1 | dip04051978 | 847 | 16th August 2003 - 10:29 PM Last post by: marke |
|||
|
Lo-Fi Version | Time is now: 1st December 2008 - 11:00 PM |