Hi I am trying to learn as much as I can about motors and starters!
I have a question, what can make the the overloads operate when a star delta three phase motor starts? |
|
|
|
Feb 9 2008, 08:12 PM
Post
#2
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,063 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello andym79
When a motor is started, it draws a very high current for the duration of the start period. The actual current and length of start time is a function of the motor design, the load torque and inertia and the starting method used, but under full voltage starting conditions, the start current will typically be between 550% and 900% of the motor rating. This overload current will cause a temperature rise in the motor and also a temperature rise in the thermal model employed by the overload relay. If the overload relay thinks that th motor is too hot, it will trip. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Feb 10 2008, 08:55 AM
Post
#3
|
|
|
Junior Member ![]() ![]() Group: Members Posts: 4 Joined: 9-February 08 Member No.: 4,273 |
Thanks,
Is it also right that overload relays can also operate due to an earth fault, undercurrent and phase imbalance? Or am I confusing my self, as on start up overload/overcurrent is the likely cause? |
|
|
|
Feb 12 2008, 01:19 PM
Post
#4
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 31 Joined: 6-September 06 Member No.: 1,906 |
Hi, as i know, overload relays will operate every time that the seting current is overpassed. The thermal protection in a overload relay will act following a curve, so if the current is not to high, it will take a time to act. The magnetic protection act inmediatley wehn a fault occurs, like an earth fault.
Chris. Thanks, Is it also right that overload relays can also operate due to an earth fault, undercurrent and phase imbalance? Or am I confusing my self, as on start up overload/overcurrent is the likely cause? |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
2 | tom | 2,076 | 29th August 2002 - 08:49 AM Last post by: GGOSS |
|||
![]() |
1 | gjnj1 | 975 | 28th September 2002 - 01:32 AM Last post by: marke |
|||
![]() |
4 | koi6456 | 1,391 | 11th November 2002 - 06:36 PM Last post by: koi6456 |
|||
![]() |
2 | GGOSS | 965 | 5th December 2002 - 08:48 AM Last post by: marke |
|||
![]() |
0 | markfoley | 898 | 26th February 2003 - 12:36 PM Last post by: markfoley |
|||
|
Lo-Fi Version | Time is now: 8th September 2008 - 01:11 AM |