How i can calculate starting current for the water booster pumps 220 kw
Go to the top of the page
 
+Quote Post
lau
post Mar 28 2008, 01:36 PM
Post #2


Junior Member
**

Group: Members
Posts: 3
Joined: 15-March 08
Member No.: 4,391



QUOTE (JONY @ Mar 23 2008, 07:24 PM) *
How i can calculate starting current for the water booster pumps 220 kw

i=220000/(1.73*420(line voltage)*0.85(pf)*0.7(eff.))
=508.874A
Go to the top of the page
 
+Quote Post
marke
post Apr 3 2008, 08:28 AM
Post #3


Posting Freak
******

Group: Moderator
Posts: 2,031
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello JONY

In order to calculate the starting current of the pumps, you need to know a number of parameters.

Firstly, the minimum start current is determined by the minimum start torque of the pumps and the ability of the motor to develop that torque, plus the start method employed.

If you start the motors on Full Voltage, they will always draw Locked Rotor Current, Independent of connected load, and will have a starting current typically in the range of 600% - 900% of the rated current of the motor.

If you use a reduced voltage starter, the current will be reduced by the voltage reduction and the torque will be reduced by the voltage reduction squared.
If you reduce the start voltage too much, you will not produce sufficient torque to start the pump.

By drawing out the speed torque curve of the pump, and overlaying the speed torque curve of the motor at different start settings, you can determine the minimum starting current of the pump and motor.
NB each motor has different starting characteristics, so the calculations need to be done for each motor.
Best regards,


--------------------
Go to the top of the page
 
+Quote Post
叱咤风云
post Jun 13 2008, 07:06 AM
Post #4


Junior Member
**

Group: Members
Posts: 2
Joined: 11-June 08
Member No.: 4,616



QUOTE (marke @ Apr 3 2008, 04:28 PM) *
Hello JONY

In order to calculate the starting current of the pumps, you need to know a number of parameters.

Firstly, the minimum start current is determined by the minimum start torque of the pumps and the ability of the motor to develop that torque, plus the start method employed.

If you start the motors on Full Voltage, they will always draw Locked Rotor Current, Independent of connected load, and will have a starting current typically in the range of 600% - 900% of the rated current of the motor.

If you use a reduced voltage starter, the current will be reduced by the voltage reduction and the torque will be reduced by the voltage reduction squared.
If you reduce the start voltage too much, you will not produce sufficient torque to start the pump.

By drawing out the speed torque curve of the pump, and overlaying the speed torque curve of the motor at different start settings, you can determine the minimum starting current of the pump and motor.
NB each motor has different starting characteristics, so the calculations need to be done for each motor.
Best regards,


very good
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   1 -ksvs29- 1,373 15th August 2002 - 09:22 PM
Last post by: marke
No New Posts   1 andromeda 1,318 14th November 2002 - 10:02 PM
Last post by: marke
No New Posts   1 -shahbaz ali- 1,726 28th August 2002 - 09:32 AM
Last post by: marke
No New Posts   0 -shahbaz ali- 1,094 --
Last post by: shahbaz ali
No New Posts   10 theDOG 1,507 25th September 2002 - 10:39 AM
Last post by: marke



RSS Lo-Fi Version Time is now: 24th July 2008 - 11:53 PM
hosted by : L M Photonics Ltd