How to determine the star Delta change over time ?
Go to the top of the page
 
+Quote Post
marke
post May 13 2008, 07:48 PM
Post #2


Posting Freak
******

Group: Moderator
Posts: 2,031
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello rseee

Do you mean the time between closing the star contactor to the change over to delta, or due you mean the time between opening the star and closing the delta contactors?

The starter should remain star connected until the motor has reaced full speed, or run out of acceleration torque. NB in many cases, the motor does not produce enough torque in star to get the load to full speed, so the changeover happens at part speed.

Have a look at Motor Starters and Star Delta Starters

Please note, the more specific the question, the better the answer, and the more likely you are to get an answer.

Best regards,
Mark


--------------------
Go to the top of the page
 
+Quote Post
rseee
post May 14 2008, 04:25 AM
Post #3


Intermediate Member
***

Group: Full Member
Posts: 13
Joined: 9-May 08
Member No.: 4,547



You means to say that the Delta changeover time to be set as per the practical conditions.
That is Time taken of the motor to reach 50% of the rated speed.
Please correct me if i understood wrong.

Go to the top of the page
 
+Quote Post
marke
post May 14 2008, 06:38 AM
Post #4


Posting Freak
******

Group: Moderator
Posts: 2,031
Joined: 24-April 02
From: Christchurch, New Zealand
Member No.: 1



Hello rseee

QUOTE
The starter should remain star connected until the motor has reaced full speed, or run out of acceleration torque

If the starter steps to delta at half speed, there will be a high start current in delta and there is no advantage of using a star delta starter over a DOL starter.

The delta change over time is set to the actual installation and it is set to change over when the motor is at full speed except where there is not enough torque to reach full speed.

Best regards,
Mark.


--------------------
Go to the top of the page
 
+Quote Post

Reply to this topicStart new topic
1 User(s) are reading this topic (1 Guests and 0 Anonymous Users)
0 Members:

 



Collapse

> Similar Topics

    Topic Title Replies Topic Starter Views Last Action
No New Posts   2 tom 1,902 29th August 2002 - 08:49 AM
Last post by: GGOSS
No New Posts   1 gjnj1 907 28th September 2002 - 01:32 AM
Last post by: marke
No New Posts   4 koi6456 1,340 11th November 2002 - 06:36 PM
Last post by: koi6456
No New Posts   0 markfoley 842 26th February 2003 - 12:36 PM
Last post by: markfoley
No New Posts   1 cpapas 899 22nd February 2004 - 12:37 AM
Last post by: marke



RSS Lo-Fi Version Time is now: 24th July 2008 - 11:49 PM
hosted by : L M Photonics Ltd