Quasi variable frequency soft start method! |
![]() ![]() |
Quasi variable frequency soft start method! |
Sep 5 2003, 12:05 PM
Post
#1
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 11 Joined: 1-September 03 Member No.: 477 |
Who got any info about this method??? I know that TRIOL corp. use it for heavy loaded induction motor start. Are any other manufacturers do the same? I know that SOLCON, Motortronics, AB, do not use this start mode.
There is no changes in a power schematics, only in software algorythm... Why no one do not realize this starting mode in their production??? |
|
|
|
Sep 5 2003, 05:41 PM
Post
#2
|
|
![]() Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 654 Joined: 22-February 03 From: USA, California Member No.: 285 |
Never heard of it.
You cannot change the output frequency without changing the power structure. Phase-angle fired SCRs are gated on, but are self commutating so the frequency output will always be the same as the fundamental. Anything else would be a VFD. If what you are thinking of is a GTO (Gate Turn Off ) thyristor system, we refer to those as 6-step or Current Source inverters. Load Commutated Inverters are frequently used for soft starting large loaded motors, but again, we consider those to be Drives, not soft starters. If you know of something new, let us know! We would love to here it. I see nothing in their website (English version) that mentions this. Being that most of us are Anglophiles, we would love to see a translation. -------------------- "He's not dead, he's just pinin' for the fjords!"
|
|
|
|
Sep 5 2003, 08:38 PM
Post
#3
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,097 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
This is a reduced version of the old cycloconverter system. By turning on different patterns for different cycles, you can effectively create subharmonic waveforms. If you have a lot more SCRs, you can create a greater number of subharmonics than when you have only six.
I think that AB were using this technique for their creep speed option some years ago, not sure, just a suspiscion. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Sep 6 2003, 10:14 AM
Post
#4
|
|
|
Intermediate Member ![]() ![]() ![]() Group: Full Member Posts: 11 Joined: 1-September 03 Member No.: 477 |
Hi all!!! Take a look at this power schematic
And one more image... This is quasi VF start method phase voltage diagramm
As we see the current frequency can be chanhed by fixed values... 1, 2, 3, 4, 5, 6, 7, 8, 10, 12, 17, 25 Hz... while voltage frequency is still 50 Hz... I think that it is usefull method... I am waiting your comments!!! ;f; |
|
|
|
Sep 6 2003, 10:31 AM
Post
#5
|
|
|
Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 2,097 Joined: 24-April 02 From: Christchurch, New Zealand Member No.: 1 |
Hello Igneous
Yes, this is a form of cycloconverter as in my last post. If you go a stage further and add SCR from each phase input to all phase outputs, i.e. 9 sets of SCRs, you have a full blown cycloconverter and can have a much better control over the pseudo frequency. The frequency is reduced by this method, but it has effectively a 50Hz carrier so ther frequncies that can be synthesised are limited, especially when you only use three SCR sets. Best regards, -------------------- Mark Empson administrator
Skype Contact = markempson | phone +64 274 363 067 LMPForum | LMP Tech Warehouse | L M Photonics Ltd | Empson family | Advanced Motor Control Ltd | LMP Software | Mark Empson Website |
|
|
|
Sep 6 2003, 09:43 PM
Post
#6
|
|
![]() Posting Freak ![]() ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 654 Joined: 22-February 03 From: USA, California Member No.: 285 |
I agree with Marke, this is a variant of the cyclo-converter system. This is exactly what AB does for their Pre-set Slow Speed feature, as well as using it in a reverse pattern for their "Smart Motor Brake". Several manufacturers including Benshaw, Motortronics and others offer it as a Jog-at-Set-Speed option but not as a complete starting ramp as suggested in the original post. It was explained to me that it tends to heat the motor windings more (per unit of torque increase) than conventional soft starters. As a result it has more limitations on starting cycles than most users are willing to accept. It is however widely used on large synchronous motors for both starting and speed control, since they are usually started less often and/or separately cooled anyway.
-------------------- "He's not dead, he's just pinin' for the fjords!"
|
|
|
|
Sep 8 2003, 01:23 AM
Post
#7
|
|
|
Senior Member ![]() ![]() ![]() ![]() ![]() Group: Moderator Posts: 404 Joined: 17-May 02 From: Melbourne Member No.: 14 |
Hello jraef & marke,
Not sure if they will ever get this one off the ground. Take a look at; http://www.acdrives.com/tec.htm The same message has been posted for over 12 months now. No joy in obtaining further information. Regards, GGOSS |
|
|
|
![]() ![]() |
Similar Topics
| Topic Title | Replies | Topic Starter | Views | Last Action | |||
|---|---|---|---|---|---|---|---|
![]() |
8 | marke | 6,572 | 3rd November 2006 - 01:00 PM Last post by: Tim |
|||
![]() |
32 | marke | 13,661 | 28th March 2008 - 01:02 PM Last post by: lau |
|||
![]() |
5 | uhaykir | 2,459 | 5th July 2002 - 09:08 AM Last post by: marke |
|||
![]() |
1 | marke | 1,065 | 19th May 2002 - 05:59 AM Last post by: marke |
|||
![]() |
1 | marke | 2,328 | 14th July 2003 - 12:44 AM Last post by: GGOSS |
|||
|
Lo-Fi Version | Time is now: 21st November 2008 - 04:00 AM |